[Bldg-sim] Window performance with frames
Andy Hoover
andyhoover at thebestconsultant.com
Fri Jul 16 06:01:09 PDT 2010
Hey all:
We do not know Alex at all but completely support his position that it is
the entire assembly/full frame in use that counts. We are a building
envelope consultancy and deal principally in the built market and see this
issue all of the time where the performance of window, storefront and
curtain wall units is dramatically different than that calculated or
provided. As a matter of fact, it is the unfortunate norm. At the end of
the day it is about actual in use performance and that performance versus
what was calculated. I will stay away from installation difference in this
one J.
Anyway, we do agree with and have seen the truth to his assessment of frame
differences. It is only the performance of the entire assembly, at every
level of a structure as a whole, that counts in the real world.
Thanks and take care,
Andy
Andy Hoover
Principal
The BEST Consultant, Inc.
Cell: 678-793-1159
Office: 678-200-7648
Fax: 678-827-0574
Email: andyhoover at thebestconsultant.com
Web: www.thebestconsultant.com
LEGAL DISCLAIMER
The information transmitted is intended solely for the individual or entity
to which it is addressed and may contain confidential and/or privileged
material. Any review, retransmission, dissemination or other use of or
taking action in reliance upon this information by persons or entities other
than the intended recipient is prohibited. If you have received this email
in error please contact the sender and delete the material from any
computer.
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Alex Krickx
Sent: Wednesday, July 14, 2010 4:57 PM
To: Otto Schwieterman; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Window performance with frames
Hi Otto,
Serious Materials provides full frame performance data here:
http://index.seriouswindows.com/document-library/Datasheets/. I have also
have some of our commercial packages modeled in curtainwall and storefront
framing systems that I can provide upon request.
Firstly let me say that Window5 is a great tool I use it often and love
it. The only thing I would advise is that there can be a wide distribution
in frame U-factors. The default U-factor for a thermally broken aluminum
(TBA) frame in Window 5 is U-1.0. Using THERM and Window5 Ive seen TBA
frame U-factors vary from as low as 0.8 to as high as 1.5. The resultant
full-frame U-factor using these 2 differing TBA frames (and the same glass
package) is: 0.29 (R-3.4) for the poorer performing frame, and 0.22 (R-4.5)
for the better frame.
I would say that putting either of those full frame u-factors in your energy
model will yield pretty different results.
I think its really important that we, as simulators and modelers, look at
full-frame performance because this is the system that will be installed in
the building. Center-of-Glass data can be useful comparing two different
glass packages, but at the end of the day, its a framed system that will be
installed and a framed system that should be analyzed. My 2¢.
Regards,
Alex Krickx
Alex Krickx
Building Energy Specialist
email_sig
1250 Elko Dr, Sunnyvale, CA 94089
(t) 408.541.8124
Warning: The information contained in this e-mail may be privileged
attorney-client communications or attorney work product and/or proprietary
and confidential. If the reader of this message is not the intended
recipient then you have received it in error and any review, distribution or
copying of this message is prohibited and you are to notify us immediately
by reply e-mail and delete the original message immediately.
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Otto
Schwieterman
Sent: Wednesday, July 14, 2010 1:10 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Window performance with frames
Does anyone know of a window manufacturer web site that has literature on
its windows including the frame? I am using Trace 700 for EA Credit 1 and
the reviewer asked for manufacturer data sheets for window performance
values (U-value, VLT and SHGC) including the frame.
Your help is appreciated,
Otto
____________________________________________________________________________
____________
Fanning/Howey Associates, Inc. intends to send this transmission (including
any attachments) only to the
designated individual or entity. If you received this message in error,
please notify the sender by replying
to the electronic mail (if electronic) or by telephone at the number
indicated on this document.
Fanning/Howey Associates, Inc. has taken reasonable precautions to ensure no
viruses are present in the
electronic mail. Fanning/Howey Associates, Inc., will not accept
responsibility for any loss or damage arising
from the use of this electronic mail or attachments. Use, disclosure,
dissemination, distribution, or reproduction
of this message by unintended recipients is not authorized and maybe
unlawful. Any information included in
this transmission that is not related to contracts with our authorization,
verbal or written, by Fanning/Howey
Associates, Inc. may not be covered by our professional liability insurance.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100716/39c1fc9b/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 5602 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100716/39c1fc9b/attachment-0001.jpeg>
More information about the Bldg-sim
mailing list