[Bldg-sim] Lighting Power Density for Labs
Nick Caton
ncaton at smithboucher.com
Thu Jun 10 08:06:46 PDT 2010
Vikram/Jorge...
I'm going to take a leap and assume we're talking about EPAct tax
deductions (not credits).
If that's the case, Section 179D (c)(2) of EPAct defines what is meant
by 90.1-2001 in the context of EPAct:
Standard 90.1-2001.--The term `Standard 90.1-2001'
means Standard 90.1-2001 of the American Society of Heating,
Refrigerating, and Air Conditioning Engineers and the
Illuminating Engineering Society of North America (as in effect
on April 2, 2003)
I bring this up because Addendum G (which revised both LPD tables
heavily) was approved by ANSI on August 6, 2003. My resulting
interpretation has been that, for the purposes of EPAct tax deductions,
the original LPD tables 9.3.1.1 and 9.3.1.2 are to be used (with the
exception of warehouses as defined by the EPAct legislation, of course).
I'd suggest using the 1.8W/SF figure, if you are doing space-by-space.
If you want to use the simpler whole-building method, you may find
University or Healthcare figures to be applicable, based on the nature
of the lab work.
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jorge
Torres-Coto
Sent: Wednesday, June 09, 2010 5:41 PM
To: 'Sami, Vikram'; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Lighting Power Density for Labs
One place to look for information is
http://www.labs21century.gov/pdf/bp_metrics_508.pdf
though this references 90.1-2004 and not 2001
Table 9.3.1.2 (page 58) for Space-by-Space Method lists Laboratory as
1.8 W/sq.ft. in the 2001 version of 90.1. Though Addendum G has the
revised Table down to 1.4 W/sq.ft
Jorge E. Torres Coto
4830 Viewridge Ave.
San Diego, CA 92123
p 858.751.0933
f 858.751.0937
c 858.688.6088
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Sami,
Vikram
Sent: Wednesday, June 09, 2010 3:02 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Lighting Power Density for Labs
I'm looking at the federal tax credit lighting requirements for a Lab
project. The problem is the ASHRAE 90.1-2001 standard that this is based
off does not have lighting requirements for labs. Does anyone know of a
good w/sf number to use as the baseline for this?
Vikram Sami, LEED AP
Sustainable Design Analyst
1382 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462 f: 404.892.5823 e: vikram.sami at perkinswill.com
www.perkinswill.com <http://www.perkinswill.com/>
Perkins+Will. Ideas + buildings that honor the broader goals of society
Years of Design Innovation
This email and any files transmitted with it are confidential and
intended solely for the addressee.
If you are not the named addressee you should not disseminate,
distribute, copy, or alter this email.
Please consider the environment before printing this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100610/9bce9eaa/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100610/9bce9eaa/attachment-0006.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1226 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100610/9bce9eaa/attachment-0007.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 14532 bytes
Desc: image006.gif
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100610/9bce9eaa/attachment-0002.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 954 bytes
Desc: image007.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100610/9bce9eaa/attachment-0008.jpeg>
More information about the Bldg-sim
mailing list