[Bldg-sim] 90.1-2007, Fan BHp and Filter Pressure Drop

Ryan Hammond RHammond at gb-eng.com
Tue Mar 23 13:30:43 PDT 2010


All,

 

A colleague brought up an interesting point about filters and fan BHp. 

 

Regarding 90.1-2007, Table 6.5.3.1.1A, Option 2, what is your
interpretation of "bhp = the maximum combined fan brake horsepower" for
an AHU?  And how does 90.1-2007 verify this?

 

90.1-2007 defines "fan system bhp" and "fan system design conditions";
however there isn't any clear mention of how exactly fan BHp is defined
with respect to filters (100% loaded filter delta-p, 66% loaded filter
delta-p, 33% loaded filter delta-p, etc.).  The fan system would still
meet capacity requirements, just at a reduced filter pressure drop as
scheduled.

 

For example, a designer could define (and schedule) the fan BHp to
operate at a max of 66% of allowable filter pressure drop for reduced
fan energy, yet schedule a fan motor to be able to meet the fully loaded
filter pressure drop.  

 

The ramifications of scheduling a lower fan BHp against 90.1-2007 is the
proposed system will now be operating more "efficiently", compared to
the baseline, assuming the filters are truly replaced at 66% of
allowable filter pressure drop (which likely would never happen in the
field!).  

 

Any thoughts on this?  Anyone on the 90.1-2007 committee that could shed
some insight?

 

Thanks,

Ryan

 

 

R. Ryan Hammond   PE, HBDP, BEMP, LEED AP

Engineer

(P) 916.921.1956 x202 

GUTTMANN & BLAEVOET Consulting Engineers

San Francisco | Sacramento | Santa Rosa <http://gb-eng.com/page/Contact>
| Website <http://www.gb-eng.com/> 

Certified Green Business <http://www.greenbiz.ca.gov/AboutUs.html>
committed to the 2030 Challenge <http://www.2030challenge.com/> 

HVAC, Plumbing, Fire Protection, Electrical, Lighting,
Telecom/Technology <http://gb-eng.com/page/services> 

Commissioning, Retro Commissioning, Energy & Building Performance
Modeling <http://gb-eng.com/page/services> 

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100323/d13fb3f8/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1953 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100323/d13fb3f8/attachment.jpeg>


More information about the Bldg-sim mailing list