[Bldg-sim] Model External Shading Devices for LEED compliance
Hisham Ahmad
hisham at edsglobal.com
Mon Mar 22 05:43:24 PDT 2010
Hi,
The baseline has to be modeled as per G3.1.5 which does not require shading
devices to be modeled. Why would you want to model them in the baseline ??
This will only compromise your energy savings.
On 22 March 2010 18:01, Lizzy Guhl <lizzy.guhl at energyarq.com> wrote:
> Thanks for the fast reply. But it is possible, anyway, to model the
> baseline building with external shading devices, right?
>
>
>
> *De:* Hisham Ahmad [mailto:hisham at edsglobal.com]
> *Enviado el:* Lunes, 22 de Marzo de 2010 7:58
> *Para:* Lizzy Guhl
> *CC:* bldg-sim at lists.onebuilding.org
> *Asunto:* Re: [Bldg-sim] Model External Shading Devices for LEED
> compliance
>
>
>
> Hi,
>
> Appendix G allows you to claim credit for shading designs/devices.
> Therefore, the baseline building is not required to have shading
> devices/projections.
>
> On 22 March 2010 17:22, Lizzy Guhl <lizzy.guhl at energyarq.com> wrote:
>
> Dear All,
>
>
>
> I am new to Leed compliance simulations and I would like to know how to
> model external shading devices in the proposed and baseline building.
> Appendix G, Table G3.1 – 5. Building Envelope, is clear about permanent
> shading devices being allowed for the proposed building. But what about the
> baseline building? Do you model the external shading devices in the baseline
> building as well?
>
>
>
> I´d appreciate any help on the matter.
>
>
>
> Regards,
>
> Lizzy
>
>
>
>
>
> LIZZY GUHL
> Dipl. Ing. (FH) Mechanical Engineering | Sustainable Design Consultant
>
>
>
> ENERGY A R Q
> Sustainability | Energy | Building Simulations | LEED®
> Member of the United States Green Building Council (USGBC)
> Chile: Juan Bautista Pastene 3120, Vitacura, Santiago | Tel. +56 2 9813142
> USA: 31 Willard St., Cambridge, MA | Tel. +1 617 710 2360
> www.energyarq.com
>
>
>
> P Consider the environment before printing this email
>
>
>
>
>
> __________ Información de ESET NOD32 Antivirus, versión de la base de
> firmas de virus 4964 (20100322) __________
>
> ESET NOD32 Antivirus ha comprobado este mensaje.
>
> http://www.eset.com
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
> --
>
> Regards
> Hisham Ahmad
>
> Energy Analyst
> Environmental Design Solutions Pvt Ltd.
> www.edsglobal.com
> New Delhi, India
> +91-9873065488
>
--
Regards
Hisham Ahmad
Energy Analyst
Environmental Design Solutions Pvt Ltd.
www.edsglobal.com
New Delhi, India
+91-9873065488
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100322/17c9cc68/attachment-0001.htm>
More information about the Bldg-sim
mailing list