[Bldg-sim] 90.1-2007, Fan BHp and Filter Pressure Drop
Chris Yates
chris at zed-uk.com
Tue Mar 23 15:58:16 PDT 2010
How does the calc apply for a fan coil system with 100% oa? Or is it
only pertinent to vav? We had some gbc comments back asking to see the
same calc for the proposed.
Sent from my iPhone
On 23 Mar 2010, at 22:49, "Rosenberg, Michael I" <michael.rosenberg at pnl.gov
> wrote:
> My opinion is that if a designer “schedules” a fan bhp to meet a
> certain static pressure requirement, and then knowing that it will a
> ctually have to meet a higher static pressure (not as a safety facto
> r but during normal operation) schedules a motor with a large enough
> nameplate hp to accommodate that, it is an attempt to get around th
> e requirement in 90.1.
>
> __________________________
>
> Michael Rosenberg
> Senior Commercial Buildings Energy Analyst
> ENERGY & ENVIRONMENT DIRECTORATE
>
> Pacific Northwest National Laboratory
> 2032 Todd Street
> Eugene, OR 97405
> (541) 844-1960
> michael.rosenberg at pnl.gov
> www.pnl.gov
>
> From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-
> bounces at lists.onebuilding.org] On Behalf Of Ryan Hammond
> Sent: Tuesday, March 23, 2010 1:31 PM
> To: bldg-sim at lists.onebuilding.org
> Subject: [Bldg-sim] 90.1-2007, Fan BHp and Filter Pressure Drop
>
>
>
> All,
>
>
>
> A colleague brought up an interesting point about filters and fan BHp.
>
>
>
> Regarding 90.1-2007, Table 6.5.3.1.1A, Option 2, what is your
> interpretation of “bhp = the maximum combined fan brake
> horsepower” for an AHU? And how does 90.1-2007 verify this?
>
>
>
> 90.1-2007 defines “fan system bhp” and “fan system design
> conditions”; however there isn’t any clear mention of how exactly
> fan BHp is defined with respect to filters (100% loaded filter delta
> -p, 66% loaded filter delta-p, 33% loaded filter delta-p, etc.). Th
> e fan system would still meet capacity requirements, just at a reduc
> ed filter pressure drop as scheduled.
>
>
>
> For example, a designer could define (and schedule) the fan BHp to
> operate at a max of 66% of allowable filter pressure drop for
> reduced fan energy, yet schedule a fan motor to be able to meet the
> fully loaded filter pressure drop.
>
>
>
> The ramifications of scheduling a lower fan BHp against 90.1-2007 is
> the proposed system will now be operating more “efficiently”,
> compared to the baseline, assuming the filters are truly replaced at
> 66% of allowable filter pressure drop (which likely would never hap
> pen in the field!).
>
>
>
> Any thoughts on this? Anyone on the 90.1-2007 committee that could
> shed some insight?
>
>
>
> Thanks,
>
> Ryan
>
>
>
> <image001.jpg>
>
> R. Ryan Hammond PE, HBDP, BEMP, LEED AP
>
> Engineer
>
> (P) 916.921.1956 x202
>
> GUTTMANN & BLAEVOET Consulting Engineers
>
> San Francisco | Sacramento | Santa Rosa | Website
>
> Certified Green Business committed to the 2030 Challenge
>
> HVAC, Plumbing, Fire Protection, Electrical, Lighting, Telecom/
> Technology
>
> Commissioning, Retro Commissioning, Energy & Building Performance
> Modeling
>
>
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100323/368f57d0/attachment-0002.htm>
More information about the Bldg-sim
mailing list