[Bldg-sim] Appendix G Chiller
Rosenberg, Michael I
michael.rosenberg at pnl.gov
Thu May 27 09:06:47 PDT 2010
Section G3.1.3.11 Heat Rejection (Systems 7 and 8) tells you that "the heat rejection device shall be an axial fan cooling tower with two speed fans." It does not matter what type of chiller you have in the proposed design, if your system type requires a chiller, it is water-cooled.
Mike
__________________________
Michael Rosenberg
Senior Commercial Buildings Energy Analyst
ENERGY & ENVIRONMENT DIRECTORATE
Pacific Northwest National Laboratory
2032 Todd Street
Eugene, OR 97405
(541) 844-1960
michael.rosenberg at pnl.gov
www.pnl.gov
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Snarski, Marty
Sent: Thursday, May 27, 2010 7:31 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Appendix G Chiller
Hello, All.
After perusing Appendix G and the LEED book, I've been unable to find the answer to this one:
If I've got a project that's using a Air-cooled Chiller, what baseline chiller do I use? Appendix G says to use 2 equally sized Screw Chillers. But, it doesn't say if these have to be air-cooled or water cooled. I'd imagine there's quite a benefit to compare with a water cooled, when you take into account the cooling tower, etc.
Any ideas if this is alright?
Martin Snarski LEED(r) AP
Mechanical Engineer
NOTICE:
This e-mail transmission is intended only for the use of the individual or entity named above and may contain information that is confidential, privileged, and/or exempt from disclosure under applicable law. If you are not the intended recipient, you are hereby notified that any review, disclosure, copying, distribution, or other use of any of the information contained in this transmission is strictly prohibited. If you have received this transmission in error, please immediately notify the sender by e-mail at the above address and delete it from your computer system; you should not copy the message or disclose its contents to anyone. The content of the message and or attachments may not reflect the view and opinions of the originating company or any party it is representing.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100527/0fef3ab0/attachment-0002.htm>
More information about the Bldg-sim
mailing list