[Bldg-sim] Really quick question
Michael A. Eustice
MAEustice at htlyons.com
Tue Nov 9 11:18:42 PST 2010
If I understand you correctly, you ran both the lighting EEM and the weather stripping EEM separately. In the lighting EEM, the gas savings got worse. In the weather stripping EEM, the gas savings got better.
Then you manually added the two together, for a net gain of gas savings (the gas savings from the weather stripping more than compensated for the gas consumption increase from the lighting EEM).
But when you run the two simultaneously, you get a different savings number. One that is better, for increased gas savings. You're wondering why.
I'm pretty sure it's because when you improved the envelope, the gas increase from the lighting reduction is not as significant. In your first run (individually) the gas increase from the lighting reduction is occurring within a lousy envelope. In the simultaneous run, the gas increase from the lighting reduction is occurring within a good envelope building, so the increase is now not as drastic. Make sense?
Michael
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Cheney
Sent: Tuesday, November 09, 2010 2:03 PM
To: John Aulbach
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Really quick question
I guess it is because the lighting generates internal loads which will benefit heating in winter. The reduction of lighting will reduce the internal loads which is more predominant than the savings from infiltration. Then you got higher gas requirement in your model.
Cheney
On Tue, Nov 9, 2010 at 10:36 AM, John Aulbach <jra_sac at yahoo.com<mailto:jra_sac at yahoo.com>> wrote:
I am doing EEM modeling, with both gas and electric effects on a multi family unit in Los Angeles.
One EEM is a lighting reduction. Another is weather stripping, which reduces infiltration.
I add up the EEMs individually and get a gas savings (negative from the lighting reduction obviously). I add them together in a COMBO run (where they interact) and the gas savings goes UP !!
WHY !!!!
John R. Aulbach, PE, CEM
Senior Energy Engineer
________________________________
Partner Energy
1990 E. Grand Avenue, El Segundo, CA 90245
W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745
www.ptrenergy.com<http://www.ptrenergy.com/> | jaulbach at ptrenergy.com<mailto:%7C%20jaulbach at ptrenergy.com>
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
________________________________
The information contained in this message is intended only for the personal and confidential use of the recipient(s) named above. If the reader of this message is not the intended recipient or an agent responsible for delivering it to the intended recipient, you are hereby notified that you have received this document in error and that any review, dissemination, distribution, or copying of this message is strictly prohibited. If you have received this communication in error, please notify HT Lyons immediately, and delete the original message.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20101109/2b0d88e0/attachment-0002.htm>
More information about the Bldg-sim
mailing list