Some good discussion about unmet hours, to summarize_
Check_
a. Occupied setpoint, unoccupied drifting point delta
b. Throttling range
c. Fan schedule conflicts with load req.
What about additional considerations like_
- Conflicting mix of zones supplied by AHU
- Extreme zone controlling thermostat
- Perimeter condition not addressed
- Water line sizing inadequate to meet flow
- Missing pumps
----------------------------
Arpan Bakshi
YRG sustainability
Direct 646.704.2880
Sent from my iPhone
On Nov 19, 2010, at 7:48 PM, Carol Gardner <cmg750 at gmail.com> wrote:
> Hi All,
>
> I think Nick is spot on in his discussion re unmet hours. While I'm
> not saying it's a wrong thing to do, I personally have never used
> oversizing the system as a way to get rid of unmet hours.
>
> As an example, I have been helping someone off the list with his
> project, a seemingly very simple building with only 5 thermal zones
> and one PVAVS air handler with dx cooling and hot water heating -
> system 5. After running my 4 exposures, and having none of them with
> any hours of unmet loads, I calculated my kW/cfm, heating load,
> cooling load, boiler kW and all of that, put the calculated results
> in the baseline, reran the baseline, and for some darn reason I had
> over 1000 hours of unmet cooling loads.
>
> I checked all my inputs, made a few changes, reran the 4 exposures,
> and not much changed. So, I put on my thinking cap and read Nick's
> email - not necessarily in that order. One of the things that
> occurred to me is that since the building is turned off all weekend
> my Monday morning pull down loads during the summer might be the
> cause of the problem, so I put in an optimum start schedule (this
> might have been required, I haven't double checked) and my unmet
> hours were reduced by about 300 hours. I had an adequate cfm/sf,
> something I'm not shy about raising at all since eQUEST defaults it
> to 0.5 cfm/sf which is usually too small, so I didn't change it.
> Then I looked at the throttling-range.
>
> For VAV systems the eQUEST/DOE2 manuals say that the throttling
> range should be at least 4 degrees to insure stable operation and
> that is what I had it at originally. After thinking about it and
> doing some simple math in my head I raised it to 6 degrees. My
> cooling temperature is set at 75 degrees so this means when my room
> temperature reads 79, set point temp + 1/2 TR + 1 degree, my cooling
> coils will be activated. Before I did this I had also looked at my
> SS-F reports and could see that my room temps weren't that far off
> from the set point temp when I had under cooled hours reported.
> Using the new throttling range brought me down to less than 500
> hours of unmet loads, which may work.
>
> So this is an example of the thinking around what's going on and
> developing a strategy that makes sense for a specific building. I
> also looked at my heating/cooling temp schedules, etc., as Nick
> mentioned. What baffles me is why, after none of my 4 exposures
> showed any unmet load hours, my baseline did. I, like Nick, have not
> had that happen before. Perhaps it has something to do with the way
> the building was zoned, 4 exposures and a core but I don't know for
> sure.
>
> Any ideas?
>
>
> Carol
>
> On Fri, Nov 19, 2010 at 2:56 PM, Nick Caton
> <ncaton at smithboucher.com> wrote:
> Hi Michael,
>
>
>
> I’d like to offer a quick heads up – your interpretation of what
> 90.1 has to say regarding addressing unmet hours is spot on and well
> -stated, no disagreements here. Neeraj however is indirectly making
> a pretty valid point that I’d hate for anyone to miss…
>
>
>
> If you only ever approach addressing unmet hours by bumping the
> oversizing factors, you may well be missing something critical. I
> for one was in this train of thought when I started out. To the
> letter of the standard, indeed this is all we’re *prescribed* to do
> to remedy the situation, but this approach will not always work, and
> may result in baseline models with a very skewed performance – suff
> ice it to say skewed is not always a *good* thing, even if it does m
> ake your performance numbers look good.
>
>
>
> Whenever I have unmet hours, I’ve learned through others on these li
> sts to investigate the “why” and “when” of those unmet hours
> as a first step. More often than not, unmet hours in my models, whe
> n they do occur, have nothing to do with lacking heating or cooling
> capacity – fan (airflow) scheduling conflicts, thermostat setpoints
> and unrealistic deadbands are the primary culprits. The systems eff
> ectively aren’t running as frequently or for a duration as they shou
> ld be.
>
>
>
> When this is the case, and I can assure Neeraj is not alone in this
> experience, fluffing the oversizing factor may appear to “remedy”
> the issue, but often as not may *not* be enough to pull your baseli
> ne/proposed models into the prescribed requirements for unmet hours.
> In some cases, you might even make the situation worse. I’m prett
> y sure the spirit of the standard, by specifying a maximum number of
> unmet hours, is to allow both the proposed and baseline systems to
> run when they need to satisfy the loads
>
>
>
> For whatever combination of reasons, and luck may be a part of it,
> it has been a long while since I’ve created an autosizing 90.1 basel
> ine model whose unmet hours did not ring in at either zero or the si
> ngle digits, and as such did not require any adjustments. I persona
> lly feel this has had a lot to do with understanding the mechanics b
> ehind what defines and can cause an unmet hour – as you’re
> getting at with consideration to drift points.
>
>
>
> As you say, future versions of 90.1 may be more nuanced, but I
> personally feel the manner in which unmet hours are currently
> addressed does a disservice to those aspiring to be quality energy
> modelers – one can easily be misled to believe an unmet load hour is
> a problem in and of itself with an easy “fix,” without
> recognizing it’s really a symptom of a problem... bumping capacities
> without first addressing the cause of unmet hours is something like
> a doctor only giving you a band-aid for a cut when what you need is
> a tetanus shot!
>
>
>
> It may be worth mentioning that my experience is dominantly within
> the world of eQuest/DOE2. I would not be surprised to find other
> engines/software have varying “typical” causes of unmet hours.
>
>
>
> Anyway, that’s my two cents, for what it’s worth =) – hope it
> might help lead others along the path!
>
>
>
> ~Nick
>
>
>
> <image001.jpg>
>
>
>
> NICK CATON, E.I.T.
>
> PROJECT ENGINEER
>
> 25501 west valley parkway
>
> olathe ks 66061
>
> direct 913 344.0036
>
> fax 913 345.0617
>
> Check out our new web-site @ www.smithboucher.com
>
>
>
> From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-
> bounces at lists.onebuilding.org] On Behalf Of Michael Collarin
> Sent: Friday, November 19, 2010 1:46 PM
> To: Nearedge; cjaigath at yahoo.com
>
>
> Cc: bldg-sim at lists.onebuilding.org
> Subject: Re: [Bldg-sim] Adjusting Capacity for Unmet Cooling
>
>
> Neeraj, it is in fact the contrary.
>
>
>
> ASHRAE 90.1-2007 Appendix G requires you to model Baseline Airflow
> Rate using a 20-degree F temperature difference between the supply
> air and room air temperatures. Therefore, if your room set point is
> 75F for cooling, set your cooling leaving air temperature to 55F and
> vice versa for heating; 72F heating set point requires a 92F leaving
> air temperature. This establishes your CFM airflow within the model.
> Do not vary these to adjust unmet hours.
>
>
>
> If you have unmet heating or cooling hours (over 300 or greater than
> 50 between baseline and proposed), you may incrementally adjust the
> baseline cooling and heating capacities (originally oversized 15%
> and 25% respectively) accordingly to reduce the overall unmet hours
> (below 300) or the difference between baseline and proposed (within
> 50).
>
>
>
> Before taking this step, be sure to look at your thermostat drift
> points. If the cooling set point is 75, but the cooling drift point
> is 84, when the space is unoccupied this would allow the space to
> move toward 84 degrees. When the space becomes occupied and the
> simulation tries to cool to 75, the system will not be able to
> achieve this within the allotted time (1 hour) and you will have an
> unmet cooling hour.
>
>
>
> There are some changes to ASHRAE 90.1-2010 that will effect unmet
> hours, but for the time being, if you are modeling a project using
> 2007 or 2004, this method should help you eliminate the unmet hours.
>
>
>
> Regards,
>
>
>
> Michael M. Collarin, EIT, LEED AP BD+C | Elm Engineering, Inc. | 212
> S Tryon St | Suite 1375 | Charlotte, NC 28281
>
> PHONE 704-335-0396 Ext. 108| FAX 704-335-0399 | www.elmengr.com
>
>
>
> From: Nearedge [mailto:near_ej at yahoo.com]
> Sent: Friday, November 12, 2010 12:51 AM
> To: cjaigath at yahoo.com
> Cc: bldg-sim at lists.onebuilding.org
> Subject: Re: [Bldg-sim] Adjusting Capacity for Unmet Cooling
>
>
>
> Hello Jaigath,
> Using the performance rating method (PRM), in my experience it is
> usually an issue of low supply CFM.
> Correct me if I am wrong but on the contrary I think that ASHARE
> baseline PRM fixes the cooling and heating capacities to 1.15 and
> 1.25 respectively and the user is allowed to bump up the supply CFM
> in increments if necessary.
> I have a feeling that the issue of unmet load hours has been
> discussed many times before -- so, the archives will be a good
> resource as well.
> Best,
> Neeraj
>
> Neeraj Kapoor
> t: +91.99581.70018
>
> e: neeraj[at]kalpakrit[dot]com
> Kalpakrit Sustainable Environments Pvt. Ltd.
> www.kalpakrit.com
>
> Office Address:
> 610-A Udyog Vihar, Phase-5,
> Gurgaon, Haryana - 122016
> t: +91.124.430.9490/ 1/ 2
> f: +91.124.430.9493
>
> Registered Address:
> 101 Anupam Apartments,
> Mehrauli-Badarpur Road,
> New Delhi - 110068
>
>
>
> On 11-11-2010 10:30, Jaigath Chandraprakash wrote:
>
> Hello All,
>
> I would like to know how other increase their baseline capacity when
> they have unmet load. I have a PSZHP system and in one system, I got
> more than 400 hrs unmet load. I usually just increase the TR cooling
> capacity until I get a lower unmet load but in this case, I think
> the unmet load is due to low supply cfm. Is it ok to adjust also the
> supply fan cfm? I am thinking that G3.1.2.2 only requires me to
> adjust only the cooling capacity. Do others adjust both cfm and
> cooling load?
>
> Thanks,
>
> Jaigath
>
>
>
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
> --
> Carol Gardner PE
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20101119/1c242312/attachment-0002.htm>
More information about the Bldg-sim
mailing list