[Bldg-sim] Ened Results analysis
Cheney
chenyu73 at gmail.com
Tue Nov 23 14:16:40 PST 2010
Hi Sambhav,
I just did a quick yet simple calculation for you as follows:
1. Assuming plant load is X
2. Assuming chiller energy requirement is Y
3. Y1= X/3.2 and Y2 = X/2.6
4. Y1/Y2 = (X/3.2) / (X/2.6) = 0.81
In this case, around 20% difference is possible.
Cheers,
Cheney
LinkedIn @ http://ca.linkedin.com/pub/yu-cheney-chen/27/637/72b
On Mon, Nov 22, 2010 at 9:28 PM, sambhav tiwari <tiwari.sambhav at gmail.com>wrote:
> Hi All,
> In one of Projects i have air cooled chillers (VAV system)
> in Proposed Case and Packaged VAV system in base Case. I defined one
> alternative of Proposed Case in which i changed VAV system to Packaged
> VAV with COP decrement of 2.6 from 3.2 of Air cooled screw chiller my
> energy consumption is going up as excepted but it is going up to 20%
> which is a matter of concern .Just by changed the HVAC system from VAV
> to PackagedVAV and reducing COP from 3.2 to 2.6 can bring 20% of
> increment is it ok?
>
> I look forward for some response
>
> Thanks
> Sambhav
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20101123/01fecc7f/attachment-0002.htm>
More information about the Bldg-sim
mailing list