[Bldg-sim] G3.1.2.5 Clarification
Julia Beabout
juliabeabout at yahoo.com
Thu Oct 28 07:26:05 PDT 2010
yes! Hear! Hear!
My experience with submitted LEED projects has been.
1. proposed and baseline use the same OA quantity
2. you can take credit for DCV in the proposed building; however, the baseline
building is also required to use DCV in the spaces that are required to have it
as prescribed in 90.1
________________________________
From: Karen Walkerman <kwalkerman at gmail.com>
To: James Hansen <JHANSEN at ghtltd.com>
Cc: bldg-sim at lists.onebuilding.org
Sent: Thu, October 28, 2010 10:12:14 AM
Subject: Re: [Bldg-sim] G3.1.2.5 Clarification
The previous discussion also touched on the topic of requirements for LEED
models changing at the review stage (your reviewer indicating something that is
reflected NOWHERE in the documentation). This really makes me mad! It requires
extra time on our end because either:
1. The reviewers are not properly educated as to the requirements
2. The reviewers are making up requirements on their own
or,
3. The reviewers are following guidelines provided to them by someone
(USGBC???) that has not been made available to the modeling professionals who
must abide by these rules.
--
Karen
On Thu, Oct 28, 2010 at 10:06 AM, James Hansen <JHANSEN at ghtltd.com> wrote:
For what it’s worth, regardless of what the various publications actually say,
the last 5-6 projects of mine have had reviewers that had me confirm that when I
use DCV in the proposed design, that the baseline design MUST match the minimum
ASHRAE 62.1-2004 (or 07) requirements.
>
>So if you don’t have DCV (shame on you!), then your baseline and proposed models
>can have matching OA, and it can be whatever quantity you want.
>As soon as you incorporate DCV, the baseline model has to go down to minimum
>62.1 rates.
>
>
>GHT Limited
>James Hansen, PE, LEED AP
>Senior Associate
>1010 N. Glebe Rd, Suite 200
>Arlington, VA 22201-4749
>703-338-5754 (Cell)
>703-243-1200 (Office)
>703-276-1376 (Fax)
>www.ghtltd.com
>
>
>From:bldg-sim-bounces at lists.onebuilding.org
>[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Karen Walkerman
>Sent: Thursday, October 28, 2010 9:57 AM
>To: Grammy
>
>Cc: bldg-sim at lists.onebuilding.org
>Subject: Re: [Bldg-sim] G3.1.2.5 Clarification
>
>There was a major discussion on this topic a few months ago, although it may
>have been on the eQuest list-serve, I don't remember. Try searching the
>archives.
>
>The general conclusion was that the current requirements are that the baseline
>and proposed design models should have the same ventilation rates, BUT that this
>doesn't make that much sense as you could over-ventilate to the point where
>there is no added benefit to the occupants, and major additional energy use.
> The discussion was primarily around LEED EA Credit 1, and there was some
>correspondence between the simulation group and the LEED credit chair. I
>believe that they will be looking at modifying this requirement for LEED models
>in the future.
>
>--
>Karen
>
>On Thu, Oct 28, 2010 at 9:32 AM, Grammy <grammy.hkust at gmail.com> wrote:
>In my opinion, the exception is means that keep the "design value" of OA same in
>both proposed and basline, but use DCV only in proposed.
>
>Because DCV can modify OA volume by the number of people in zone, and the OA
>requirement is dynamics in simulation - which is too hard to keep baseline same
>with, and also should not keep the same, if not where does the saving come
>from?
>
>On Thu, Oct 28, 2010 at 9:24 PM, Paul Riemer <Paul.Riemer at dunhameng.com> wrote:
>Section G.3.1.2.5 in 90.1-2007 has added an exception to the "shall be the same"
>for models with demand controlled ventilation in the proposed that is not
>required by Section 6.4.3.9.
>
>
>That alone is kind of confusing since it does not address what the values should
>be when they are allowed to not be the same.
>
>
>I think they are trying to resolve the intersection of projects that use more OA
>than Std 62.1 and utilize demand controlled ventilation.
>The most recent Trane Engineers broadcast promised more changes coming to this
>section (as addendum DA?) but I do not have anything published to reference.
>
>Paul Riemer
>Dunham
>
>
>From:bldg-sim-bounces at lists.onebuilding.org
>[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Kingsley, Michael
>L.
>Sent: Thursday, October 28, 2010 7:50 AM
>To: Grammy; Jaigath Chandraprakash
>
>Cc: bldg-sim at lists.onebuilding.org
>Subject: Re: [Bldg-sim] G3.1.2.5 Clarification
>
>I agree. Standard 61.1 sets the minimum acceptable ventilation rate. The
>design ventilation rate can be higher, and the baseline rate should be the same
>as the real design.
>
>Best regards,
>
>Mike
>
>Michael L. Kingsley, PhD, PE, LEED AP | R. W. Beck, An SAIC Company
>Senior Engineer/Project Manager
>Energy, Environment & Infrastructure Solutions
>office: 315.437.1869 x205 | mobile: 315.373.4081
>
>
________________________________
>From:bldg-sim-bounces at lists.onebuilding.org
>[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Grammy
>Sent: Thursday, October 28, 2010 8:38 AM
>To: Jaigath Chandraprakash
>Cc: bldg-sim at lists.onebuilding.org
>Subject: Re: [Bldg-sim] G3.1.2.5 Clarification
>
>In my opinion:
>
>For LEED, the OA should increase 30% first. This is the propose requirement.
>
>Then for energy model, the baseline model should equal to proposed, which means
>the baseline OA is also 30% more than 62.1 requirement.
>
>On Thu, Oct 28, 2010 at 6:07 PM, Jaigath Chandraprakash <cjaigath at yahoo.com>
>wrote:
>Hello,
>
>G3.1.2.5 states that minimum ventilation rates will be the same for proposed
>building and baseline building. Does it mean that if my building design OA rate
>is increased by 30%, my model will still be based on the minimum OA required by
>62.1 and is still equal to the baseline building OA? Meaning my proposed
>building wont be penalized by supplying more OA?
>
>
>Thanks in advance.
>
>
>Jaigath
>
>
>_______________________________________________
>Bldg-sim mailing list
>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>To unsubscribe from this mailing list send a blank message to
>BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>_______________________________________________
>Bldg-sim mailing list
>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>To unsubscribe from this mailing list send a blank message to
>BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
________________________________
The information contained in this communication is confidential, may be
privileged, and is intended only for the use of the addressee. It is the
property of GHT Limited. Unauthorized use, disclosure or copying of this
communication or any part thereof is strictly prohibited and may be unlawful.
If you have received this communication in error, please notify me immediately
by return e-mail or by e-mail to ght at ghtltd.com, and destroy this communication
and all copies thereof, including all attachments. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20101028/481677a3/attachment-0001.htm>
More information about the Bldg-sim
mailing list