[Bldg-sim] Modeling fume hood exhausts
Gerald Pde
geraldpde at yahoo.com
Wed Sep 1 02:37:42 PDT 2010
Peter,
I think as Vikram mentioned, it depends on the total exhaust (cumulative exhaust
of all the fume hoods). If the total exhaust exceeds 15,000cfm, then the
baseline needs to have AT LEAST one of the following:
1. VAV hood exhaust till a 50% min turn down over the total CFM. Hence you could
only take advantage of a lower VAV set point on the actual equipment.
2. Make-up air. Separate make-up air with supply temperature very close to room
temperatures.
3. Heat recovery . If the building has both VAV and HR, then you should be able
to take full benefits of heat recovery or vise-versa.
Hence if your total fume hood exhaust is lower than 15,000 cfm, then you should
be able to take advantage of VAV fume hood exhaust over constant volume
exhaust.
Does this make sense?
Gerald
________________________________
From: Peter Simmonds <peter.simmonds at ibece.net>
To: Aleka Pappas <APappas at enermodal.com>; bldg-sim at lists.onebuilding.org
Sent: Wed, September 1, 2010 3:39:42 AM
Subject: Re: [Bldg-sim] Modeling fume hood exhausts
Thanks for all the help. Here is another angle I am coming from.
Assuming the base case were to be a traditional fume hood exhaust system which
used constant volume fans in order to create the 3000 fpm discharge velocity. If
the fume hoods have sash control the there is an outside air by-pass on the fan
header, so down stream VAV and upstream constant volume exhaust fans. I know
these constant volume fans can be staged to form a 'quasi' variable exhaust. So
if this were the base case then one could apply the list of various innovations
on how to apply variable exhaust flow to the proposed model.
The ASHRAE 90.1 6.5.7.2 isnt really a solution, however Aleka you mention Lab
21, have you had any luck in getting this accepted by the LEED meanies?
Peter Simmonds,Ph.D.
Senior Associate
IBE Consulting Engineers
14130 Riverside Drive, Suite 201
Sherman Oaks, CA 91423
p: (818) 377-8220 x246f: (818) 377-8230
www.ibece.com
Ideas for the built environment
This e-mail message, including any attachments, is for the sole use of the
intended recipient(s) and may contain confidential and privileged information.
Any unauthorized review, use, disclosure, or distribution is prohibited. If you
are not the intended recipient, please contact the sender by reply e-mail and
destroy all copies of the original message.
From:Aleka Pappas [mailto:APappas at enermodal.com]
Sent: Tuesday, August 31, 2010 2:41 PM
To: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Modeling fume hood exhausts
I just spent a while digging through all the latest docs on modeling labs for a
LEED analysis (90.1-2004, 90.1-2007, addenda, & Labs 21). This is my
interpretation:
* If the building has fume hood exhaust over 15,000 cfm, the Baseline
system is VAV, and exhaust is turned down to at least 50% for unoccupied
hours. I am modeling the unoccupied turn down rate the same in the
Baseline as in the Proposed models, because how low it can go at night
depends on the type of lab (ie: the project doesn't get more credit for
turning down to 20%). This is from Labs 21, and 90.1 (2004 or 2007)
section 6.5.7.2.
* A project can claim energy savings for demand controlled fume hoods
during occupied hours if the controls are automatic (Labs21 has some
schedules for guidance in modeling this).
* Energy recovery is not modeled in the Baseline (see 90.1-2007 G3.1.2.10
Exception h).
Let me know if you have a different interpretation....I don't think all these
issues are laid out in detail for modelers yet.
Aleka Pappas
Building Energy Engineer
ENERMODAL ENGINEERING, INC.
Inspiring energy and resource efficient buildings.
www.enermodal.com
1325 E. 16th Ave.
Denver, CO 80218
APappas at enermodal.com
Office: 303.861.2070/ Direct: 720.221.1082
On 8/31/2010 12:35 PM, varun kulkarni wrote:
I think it also depends on the software you are using to model a fume hood.
Because if exhaust is specified more than the supply due to the hood, the
software may disregard the lower supply and equate the higher value of exhaust
to the supply. I am also trying to model a VAV exhaust fume hood and facing a
lot of problems doing it. So you have to figure out a way to control you exhaust
by altering your VAV supply.
If you know some other way, please let me know also :)
On Tue, Aug 31, 2010 at 2:23 PM, Sami, Vikram <Vikram.Sami at perkinswill.com>
wrote:
I think that depends on the total volume of exhaust. I don't have it in front of
me, but I think if your exhaust is more than a certain amount you have to have
either energy recovery to fifty percent or vav flow.
Sent from a mobile device
-----Original Message-----
From: Peter Simmonds [mailto:peter.simmonds at ibece.net]
Sent: Tuesday, August 31, 2010 12:09 PM Central Standard Time
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Modeling fume hood exhausts
Can anyone tell me when modeling a lab system with fume hoods as to whether the
baseline systems are to be modeled as constant volume?
(subsequent alternatives will have variable volume fume hoods).
Peter Simmonds,Ph.D.
Senior Associate
IBE Consulting Engineers
14130 Riverside Drive, Suite 201
Sherman Oaks, CA 91423
p: (818) 377-8220 x246 f: (818) 377-8230
www.ibece.com<http://www.ibece.com/>
Ideas for the built environment
This e-mail message, including any attachments, is for the sole use of the
intended recipient(s) and may contain confidential and privileged information.
Any unauthorized review, use, disclosure, or distribution is prohibited. If you
are not the intended recipient, please contact the sender by reply e-mail and
destroy all copies of the original message.
This email and any files transmitted with it are confidential and intended
solely for the addressee. If you are not the named addressee you should not
disseminate, distribute, copy, or alter this email.
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
--
Thanks and Best Regards,
Sincerely,
Varun Kulkarni , M.S. , EIT
RMF Engineering
5520, Research Park Drive, Suite 300
Baltimore, MD - 21228
Office : 410-576-0505 ext. 5352
Mobile: (+1)405-385-1928
Note: Please do not print, unless required.
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100901/c4ce96be/attachment.htm>
More information about the Bldg-sim
mailing list