[Bldg-sim] A Question about chilled water usage
John Aulbach
jra_sac at yahoo.com
Fri Sep 10 16:28:16 PDT 2010
Vikram:
I agree with James. Chiller energy would be measured in electric or gas units
(energy input)..
Ton-hours is a load (useful energy) function.
John R. Aulbach, PE, CEM
Senior Energy Engineer
________________________________
PartnerEnergy
1990 E. Grand Avenue, El Segundo, CA 90245
W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745
www.ptrenergy.com| jaulbach at ptrenergy.com
________________________________
From: "James V Dirkes II, PE" <jvd2pe at tds.net>
To: "Sami, Vikram" <Vikram.Sami at perkinswill.com>;
"bldg-sim at lists.onebuilding.org" <Bldg-sim at lists.onebuilding.org>
Sent: Fri, September 10, 2010 2:30:19 PM
Subject: Re: [Bldg-sim] A Question about chilled water usage
Dear Vikram,
I think that the definition of ton-hours is inherently an “cooling energy
delivered” or “useful energy”, metric.
The Building Performance Team
James V. Dirkes II, P.E., LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653
From:bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Sami, Vikram
Sent: Friday, September 10, 2010 4:23 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] A Question about chilled water usage
I’m looking at utility data for a building on a college campus that has a
central utility plant. They list cooling energy in ton-hrs and It seems really
high for all buildings across the board.
However – if you assume that ton-hrs is the metered chilled water usage and not
the chiller energy, its not that bad. For example if the chilled water usage is
1 ton-hrs, that’s 12,000 BTU’s of cooling energy delivered. However, if whats
being measured is chilled water usage (and not chiller energy), then 1 ton-hr is
not the energy consumed by the chiller – that should be 12,000BTU/COP of the
chiller. So if the chiller COP is 4 – then that’s only 3,000 BTU’s of energy
consumed to deliver that ton-hr.
So – to get to the point – does anyone know if campuses monitor their chilled
water usage (in ton-hrs) as chiller energy or cooling delivered?
(I hope this makes snese)
Vikram Sami, LEED AP
Sustainable Design Analyst
1382 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462 f: 404.892.5823 e: vikram.sami at perkinswill.com
www.perkinswill.com
Perkins+Will. Ideas + buildings that honor the broader goals of society
Years of Design Innovation
This email and any files transmitted with it are confidential and intended
solely for the addressee.
If you are not the named addressee you should not disseminate, distribute, copy,
or alter this email.
Please consider the environment before printing this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100910/3522d7be/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 954 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100910/3522d7be/attachment-0002.jpeg>
More information about the Bldg-sim
mailing list