[Bldg-sim] Core and Shell Office Modelling
Shanta Tucker
shanta.tucker at atelierten.com
Thu Apr 7 07:18:45 PDT 2011
Hello Jaigath,
My suggested answers follow your questions.
1. Does that mean I will be modeling only the common since it only the areas that were designed? No. You must model the whole building and site.
2. Do I need to also include the tenant areas? Yes, include the tenant spaces.
3. Since the tenant areas have FCU pipe provision, do I model it as FCU or do I have to model it as system 6 which is my baseline case? You may model the tenant spaces with FCU's in the proposed model so long as you have an engineering drawing for a typical floor showing this; if you don't have this I suggest that you ask for it. If that is not possible to obtain, perhaps a narrative from the engineer of record or the tenant lease would suffice, but I'm not 100% sure if it would. In my opinion, you'll need to provide some documentation that the tenants must install the FCU's in order to help the GBCI reviewers understand the argument why you are modeling FCU's and not system 6.
--
Shanta Tucker
Atelier Ten
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jaigath Chandraprakash
Sent: Thursday, April 07, 2011 7:21 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Core and Shell Office Modelling
I am simulating a core and shell office building with system 6 for my baseline. The design case is a two pipe fan coil units at common areas and all tenants will have chilled water pipe provision for them to tap their fan coil units. Based in CS Appendix 6 under step 1, model the HVAC system as described in the design documents. My question is:
1. Does that mean I will be modeling only the common since it only the areas that were designed?
2. Do I need to also include the tenant areas?
3. Since the tenant areas have FCU pipe provision, do I model it as FCU or do I have to model it as system 6 which is my baseline case?
Thank you all in advance.
Jaigath
________________________________________________________________________
This e-mail has been scanned for all viruses by Star. The
service is powered by MessageLabs. For more information on a proactive
anti-virus service working around the clock, around the globe, visit:
http://www.star.net.uk
________________________________________________________________________
______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110407/4c371e48/attachment-0002.htm>
More information about the Bldg-sim
mailing list