[Bldg-sim] Modeling Centralized Water-to-Water HP's and Hybrid HP's
Aaron Smith
asmith at mreng.ca
Mon Aug 8 15:02:34 PDT 2011
Ahmed,
The best recommendation that I can think of is to model this as a
"Combination Ground Source Heat Pump" Plant with a "4 pipe fan coil" System.
You will have to add the distributed heat pump cooling capacities to the
central heat pump cooling capacity and create a representative COP. As you
can't model a boiler plant for the System heating, I'd recommend modeling
the heating as a Natural Gas or Oil Furnace. System Cooling can be input as
Hydronic so chilled water will come from the central Water-to-water heat
pump plant. NRCan may be willing to provide input as well even with the
ecoENERGY program ending this past spring.
As you know EE4 is not the most flexible simulation program, eQUEST might do
a better job if you are familiar with that software.
Regards,
Aaron
Aaron Smith, P.Eng
LEEDR AP BD+C, M-ASHRAE, Mechanical Engineer
t: (902) 422-7393
f: (902) 423-4945
e: <mailto:asmith at mreng.ca> asmith at mreng.ca
The electronic message contained herein is private and confidential,
intended only for the recipient(s) specified. If you have received this
message in error, please delete it and notify us immediately. Any
accompanying files are supplied as a matter of courtesy only. The data are
without warranty of any kind. Any person or business making use of the data
is responsible for confirming its accuracy and completeness. M&R
Engineering Ltd. is not responsible for edited or produced versions of this
digital information.
_____
From: Mehta, Gaurav [mailto:Gaurav.Mehta at stantec.com]
Sent: Thursday, August 04, 2011 7:06 PM
To: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Modeling Centralized Water-to-Water HP's and Hybrid
HP's
Ahmed,
Have you referenced the EE4
<http://canmetenergy-canmetenergie.nrcan-rncan.gc.ca/fichier/79060/EE4-Engli
sh-2008-02-01.pdf> Modeling Guide ?
In case you have not. You might find it useful when using EE4. It has a
number of workarounds with examples.
Thanks.
Best regards,
Gaurav
Gaurav Mehta, LEEDR AP BD+C
Sustainable Building Analyst
Stantec
1932 First Avenue Suite 307
Seattle WA 98101
Ph: (206) 770-7779
Fx: (206) 770-5941
Gaurav.Mehta at stantec.com
<http://www.stantec.com> stantec.com
The content of this email is the confidential property of Stantec and should
not be copied, modified, retransmitted, or used for any purpose except with
Stantec's written authorization. If you are not the intended recipient,
please delete all copies and notify us immediately.
* Please consider the environment before printing this email.
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Ahmed Azhari
Sent: Thursday, August 04, 2011 2:12 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Modeling Centralized Water-to-Water HP's and Hybrid HP's
Hi,
I am using a Canadian-based energy modeling software called EE4 which uses
DOE calculation engine. I am trying to model a centralized water-to-water
Heat Pumps System that provides hot water to distributed hybrid heat pumps
(hybrid heat pump is fan coil in heating mode and heat pump in cooling
mode). The hybrid heat pumps uses ground to reject heat when in cooling
mode. The centralized water-to-water heat pumps provide chilled water for
the make-up air units cooling coils. The Make-up air units heating coils are
fed directly from the boiler. EE4 would not allow me to use a combination of
these two systems. Does anyone have a work-around to this type of system.
I would really appreciate any input in this regards.
Thanks,
Ahmed
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110808/b898b500/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1860 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110808/b898b500/attachment-0002.jpg>
More information about the Bldg-sim
mailing list