[Bldg-sim] F-Factor
Dahlstrom, Aaron
ADahlstrom at in-posse.com
Wed Aug 24 21:38:41 PDT 2011
Joshua -
Confining my comments to eQUEST:
There appears to be a quick shortcut we've tried on some models:
eQUEST appears to create virtual materials with virtual R-vals to turn the UA product into the appropriate F-Perim product anticipated by ASHRAE.
This step occurs when exiting the Wizard mode - ie pushing the "Finish" button.
Floor slabs specified as slabs-on-grade will often have a virtual material in their layer definition - this virtual material's resistance will vary, and I believe it may be varying based on the ratio of perimeter to surface area.
If you've done all your zoning within the wizard, then it is possible to get eQUEST to automatically generate the different "virtual material" resistance factors for each of the different room's slab surfaces, if you need to vary slab insulation, and if the slab insulation options available in the Wizard include the option you're looking for.
Assuming you've left wizard mode, you can save the project as a separate file name (so as not to over-write any detailed edit changes), re-enter Wizard mode, reselect the slab insulation you would like, and "Finish" the wizard. The virtual material resistances will have changed. Then these virtual resistances can be copied to the virtual materials you have in the "real" detailed data edit file.
A caution - I haven't validated that this produces the exact correct factors to translate eQUEST's modeled area into the
Has anyone else on the list looked into this procedure?
Aaron Dahlstrom , PE, LEED(r) AP
In Posse - A subsidiary of AKF| 1500 Walnut Street, Suite 1414, Philadelphia, PA 19102
d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF: 215-735-7290
e: ADahlstrom at in-posse.com | in posse web: www.in-posse.com<http://www.in-posse.com/> | akf web: www.akfgroup.com<http://www.akfgroup.com/>
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Talbert, Joshua
Sent: Wednesday, August 24, 2011 10:49 AM
To: bldg-sim at lists.onebuilding.org
Cc: Neuburger, Bill
Subject: [Bldg-sim] F-Factor
Hello Bldg Sim Folks,
Could anyone comment on how they "translate" the F-factor requirement for on grade slabs into a U-value / material for a floor construction in Energy+ or eQuest
My method has always been to create a fictional material with negligible thickness that approximates the equivalent R-value for the whole floor area of the zone based on the edge requirement. This results in me creating a separate one of these fictional materials for each zone. This is because even though a zone might have the same F-factor requirement the difference in perimeter to floor area ratio effects the actual heat flux through the floor, or so I think.
Here is an example of how I have modeled this, see attached picture for a layout:
[cid:image001.png at 01CC62BF.562F7C90]
F-Factor = 0.64 (equivalent to R-10 insulation for 48" and for an "Unheated Slab" per ASHRAE 90.1 Table A6.3)
Zone 1
Area = 25 sqft
Edge Perimeter = 10 ft
Zone 2
Area = 375 sqft
Edge Perimeter = 70 ft
Perimeter * F factor = Area * U value equivalent
Zone 1 equivalent U = 0.256
Zone 2 equivalent U = 0.119
This process has made sense to me, but in reviewing this technique with a colleague we wondered what does everyone else do. Am I under/over predicting slab loss for certain zones with this method? Your comments and insight are always appreciated.
Thanks,
Josh
Joshua W. Talbert P.E., LEED-AP
Mechanical Engineer
Hallam///ICS
38 Eastwood Dr. Suite 200
S. Burlington, VT 05403
P: (802) 658-4891
F: (802) 658-1457
________________________________
CONFIDENTIALITY NOTICE:
The information contained in this transmission, as well as any accompanying documents, constitutes confidential and/or legally privileged information which is the property of Hallam-ICS. The information is intended solely for the individual entity named on this transmittal sheet. If you are not the designated recipient, you are hereby notified that any disclosure, copying, distribution or taking any action in reliance on this information is strictly prohibited. If you received this in error, please contact the sender and delete the material from any computer. Opinions, conclusions and the information in this message that do not relate to the official business of my firm shall be understood as neither given nor endorsed by it.
This e-mail may contain information that is confidential, privileged or otherwise protected from disclosure. If you are not an intended recipient of this e-mail, do not duplicate or redistribute it by any means. Please delete it and any attachments and notify the sender that you have received it in error. Unintended recipients are prohibited from taking action on the basis of information in this e-mail. E-mail messages may contain computer viruses or other defects, may not be accurately replicated on other systems, or may be intercepted, deleted or interfered without the knowledge of the sender or the intended recipient. If you are not comfortable with the risks associated with e-mail messages, you may decide not to use e-mail to communicate with In Posse.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110825/35061c05/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 10188 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110825/35061c05/attachment-0002.png>
More information about the Bldg-sim
mailing list