The CIR is wrong and is in direct contradiction to Appendix G and the Energy
Modeling Guide for LEED.
I have never seen a reviewer cite this CIR in a review.
Marcus Sheffer
Energy Opportunities, Inc/a 7group Company
1200 E Camping Area Road, Wellsville, PA 17365
717-292-2636, <mailto:sheffer at sevengroup.com> sheffer at sevengroup.com
www.sevengroup.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jackson, Alan
Sent: Monday, February 28, 2011 9:26 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] existing envelope CIR
Is anyone aware of this CIR being upheld?
12/10/2008 - Credit Interpretation Request
The team is requesting that you please verify the meaning of the sentence in
ASHRAE 90.1, Table G3.1 regarding baseline
envelope requirements for existing buildings.."For existing building
envelopes, the baseline building design shall reflect existing
conditions prior to any revisions that are part of the scope of work being
evaluated". Please confirm if this means that the walls, roof,
windows, etc for the baseline is to be modeled to match the existing
conditions NOT according to the values in Table 5.5-1 thru 5.5-
8.
2/20/2009 - Ruling
If an existing envelope component is untouched, the baseline is as that
component exists. However, if an existing component is
modified, the baseline needs to meet the requirements for alterations in
Section 5.1.3.
It indicates that when modifying the existing envelope, the baseline needs
to meet the minimum requirements of Chapter 5.
Have users in the group received comments from the reviewers when trying to
model modified envelopes at the existing performance values, because all
language regarding this issue other than the CIR indicate that existing
envelopes get to be modeled at existing performance conditions regardless of
any alterations.
Thanks
Alan Jackson, LEED AP
HVAC Project Engineer / BIM Team Leader
KlingStubbins
2301 Chestnut Street
Philadelphia, Pennsylvania
19103
P 215.569.2900, ext. 3380
F 215.569.5963
E ajackson at klingstubbins.com <mailto:jdoe at klingstubbins.com>
W www.klingstubbins.com <http://www.klingstubbins.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110228/e730fc30/attachment-0001.htm>
More information about the Bldg-sim
mailing list