Mon Jan 31 09:50:51 PST 2011
Hi Karen,
My understanding is that the statement will apply beyond system 1-2.
Whenever a HVAC system is defined in EER, it is necessary to separate supply
fan energy from cooling energy.
Supply fan energy = (gross cooling - net cooling)/3.413
and
COP = gross cooling /[(total input power - fan power) x 3.413]
Does it make sense?
Regards,
Cheney