[Bldg-sim] ASHRAE Appendix G EER Calculation
Nick Caton
ncaton at smithboucher.com
Mon Jan 31 14:58:18 PST 2011
Mr. Sam is referencing/providing:
User's Manual for ANSI/ASHRAE/IESNA Standard 90.1-2007
Example 11-C "Calculating COP for Compressor and Condenser"
(Found on page 11-18)
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Arpan
Bakshi
Sent: Monday, January 31, 2011 4:48 PM
To: Sam Mason
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] ASHRAE Appendix G EER Calculation
Sam
Great example. Would you kindly provide a detailed citation, so it is
recorded in the archives.
Thanks
Arpan
On Mon, Jan 31, 2011 at 5:30 PM, Sam Mason <sam.mason at atelierten.com>
wrote:
Karen,
>From the user's guide, the fan power should be removed from the standard
EER rating of packaged cooling systems. Excerpt below but let me know if
you have any further questions.
A 15-ton packaged rooftop single-zone system having an EER of 8.6 (COP
of 2.5) is
specified for a building. The following table gives the design
specifications. How should
this be modeled?
Equipment parameter Value
Net Cooling Capacity (Btu/h) 174,000
Total Packaged Unit Input Power (W) 20,128
EER 8.64
Gross Cooling Cap (ARI conditions) 182,000
A
The supply fan power is the difference between the gross and the net
cooling capacity.
Supply Fan Power = (182,000 - 174,000 Btu / h) / 3.413 Btu /W h = 2343
W
>From the equation for cooling system COP, the cooling provided by the
compressor and
the condenser into the airstream in Btu/h per Btu/h of electrical power
input is:
COP = (182,000 Btu / h) / {(20,128 - 2343 W)* 3.413 Btu / W h } = 3.0
Some simulation programs use an energy input ratio (EIR), which is
1/COP. In this case,
the EIR for this piece of equipment would be 1/3 or 0.333.
--
Sam Mason
Atelier Ten
T +1 212 254 4500 x221
From: bldg-sim-bounces at lists.onebuilding.org [mailto:
bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Karen Walkerman
Sent: Monday, January 31, 2011 3:53 PM
To: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] ASHRAE Appendix G EER Calculation
A clarification:
My question pertains to baseline models, with baseline systems.
--
Karen
On Mon, Jan 31, 2011 at 12:09 PM, Karen Walkerman <kwalkerman at gmail.com>
wrote:
Hi All,
G3.1.2.1 in ASHRAE 90.1 says that "Where efficiency ratings, such as EER
and COP, include fan energy, the descriptor shall be broken down into
its components so that supply fan energy can be modeled separately."
However, I am a little unclear as to which baseline systems this applies
to. It seems that it would apply to systems 1 - 2, and not to systems 3
- 8?
Thanks,
--
Karen
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110131/eb3e68ab/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110131/eb3e68ab/attachment-0002.jpeg>
More information about the Bldg-sim
mailing list