[Bldg-sim] Simulating VRV/VRF systems
Kevin Kyte
KKyte at watts-ae.com
Thu Jul 21 08:00:49 PDT 2011
I believe a dedicated VRF module was released this year for energyplus. I have not used it though and cannot comment further.
Kevin
From: Smith, Michael [mailto:michael.smith at wspfk.com]
Sent: Thursday, July 21, 2011 10:19 AM
To: Vinay Devanathan; bldg-sim at lists.onebuilding.org; EnergyPlus_Support at yahoogroups.com
Subject: Re: [Bldg-sim] Simulating VRV/VRF systems
Vinay
Simulating the VRV/VRF as a WSHP is effectively what the PVVT approach is modeling; it uses a heat pump as the heating source and can be set to water cooled. The PVVT allows for more complexity and control in how the water source heat pump operates. (i.e. variable speed compressor) See the attached presentation put together by Dana Troy and Mark Denyer, it’s quite helpful in their explanation.
Cheers,
Michael J. Smith, EIT, LEED® AP
WSP ▪ FLACK + KURTZ
512 Seventh Avenue, New York, NY 10018
Direct: 212.951.2671 | Main: 212.532.9600
www.wspfk.com<http://www.wspfk.com/>
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Vinay Devanathan
Sent: Wednesday, July 20, 2011 6:12 PM
To: bldg-sim at lists.onebuilding.org; EnergyPlus_Support at yahoogroups.com
Subject: [Bldg-sim] Simulating VRV/VRF systems
Hello All,
I have come across the PVVT modeling approach as a workaround for simulating VRV/VRF Systems in eQuest.
I was wondering why the workaround of using Water-source Heat Pumps to mimic a VRV/VRF system has not been proposed as yet.
Any explanation/reasoning would be much appreciated.
Thank you.
Vinay
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110721/8981e24d/attachment-0001.htm>
More information about the Bldg-sim
mailing list