Nick Caton
ncaton at smithboucher.com
Wed Jun 1 07:54:24 PDT 2011
Hi Ben,
If you want the quantity/capacities of your modeled systems to match the
scheduled equipment, you should match the actual zoning.
Combining zones pretty much requires combining systems, as far as I
know... this is a by-product of the "1 system per zone" rule for DOE2.
"Too large" is relative - you could explain the system is an
approximation/sum of multiple heat pumps working together... but if you
are documenting the model extensively (i.e. LEED), you may find it less
work in the long haul to invest some extra time setting up the zoning
geometries accurately to start. That's my standard practice for heavily
documented projects.
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Ben
Pressman
Sent: Wednesday, June 01, 2011 8:49 AM
To: bldg-sim; equest-users at lists.onebuilding.org
Subject: [Equest-users] WSHPs in eQUEST
Greetings everyone,
I am relatively new to this list, and have been using eQUEST for only
about a year. I am modeling a 3-story office building with water-loop
heat pumps, but information from the building owner, architect, and
engineer are very limited.
The WSHPs are single-zone (as far as I know) and there are tons of them.
In eQUEST, do I have to create a separate zone for each one? If I make
larger zones (eg. grouping together perimeter offices), it creates heat
pumps that are too large. Is there any way to simplify the zoning and
retain the proper heat pump size and number?
Ben Pressman, EIT, BESA
Project Engineer
Practical Energy Solutions
770 e. market street, suite 250
west chester, pa 19382
ph: 610.430.1382
fax: 610.430.1375
cell: 610.733.9518
web: http://www.practicalenergy.net <http://www.practicalenergy.net/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110601/1e8a2c7e/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110601/1e8a2c7e/attachment-0002.jpeg>
More information about the Bldg-sim
mailing list