Hi Marcus,

Thanks for asking us for our feedback.  I welcome this opportunity to give
you some information regarding my experience as a LEED modeler and some
ideas I have for making the modeling part more useful.

Many of the LEED projects I work on do not use LEED as a design tool.  For
these projects, even though my initial proposal includes schematic design
and design development modeling, I am usually asked to complete only the
final LEED model and LEED model documentation, ie "please do only what is
required for LEED."  This means that the modeling tool is not being used to
make design decisions.

I like that the new EA C1 language talks about using energy modeling to
inform design decisions, and I think that it would be helpful to engage this
list-serve to determine the best way to bring that goal into the LEED
requirements.  One thing that comes to mind is that I use many tools during
design development phase energy modeling.  Often, I'll complete thermal
modeling of building envelope details in order to help the architect reach
achieve a higher overall R-value for envelope constructions.  While not a
whole-building energy analysis, this is often one of the most illuminating
discussions I have with architects.  Often I will run a simple model with
R-20, R-30 and R-40 walls, we'll look at overall energy use differences and
the engineer will look at benefits to system sizing and then the major
conversation is: how do we construct the building so that we actually
achieve an overall R-value that meets our goals, not just in the center of
the wall.

Sometimes I prepare a detailed report for model alternatives, the best
results come from sitting down with the design team, running a number of
alternatives and viewing and discussing results all at the same time.  The
LEED documentation requirement for this portion of the credit should be
similarly flexible.

Thanks for your time,

--
Karen

On Sun, May 15, 2011 at 8:50 PM, Marcus Sheffer <
sheffer at energyopportunities.com> wrote:

>  Yes I think it is the same study which showed LEED buildings were 25% to
> 30% more energy efficient than average.  There was considerable debate about
> the interpretation of the data.
>
>
>
> The purpose of my post was how do we get folks to use modeling on LEED
> project to make them more energy efficient.  Some folks just complain about
> LEED without offering a better alternative.  USGBC is seeking your good
> ideas to make it better, more useful and effective.
>
>
>
> Marcus Sheffer
>
> Energy Opportunities, Inc/a 7group Company
>
> 1200 E Camping Area Road, Wellsville, PA  17365
>
> 717-292-2636, sheffer at sevengroup.com
>
> www.sevengroup.com
>
>
>
> *From:* Hussein Abaza [mailto:ahussein at spsu.edu]
> *Sent:* Saturday, May 14, 2011 8:47 PM
> *To:* Marcus Sheffer
>
> *Cc:* bldg-sim at lists.onebuilding.org
> *Subject:* Re: [Bldg-sim] Energy Model Cost - best design doesn'tequalmost
> LEED points
>
>
>
> There is a famous study ( I don't recall the link to it) which shows that
> almost 50% of LEED buildings consume as much and more energy than non LEED
> buildings.
> ----- Original Message -----
> From: "Marcus Sheffer" <sheffer at energyopportunities.com>
> To: "Julia Beabout" <juliabeabout at yahoo.com>, "Nick Caton" <
> ncaton at smithboucher.com>, "Hussein Abaza" <ahussein at spsu.edu>, "Bill
> Bishop" <wbishop at pathfinder-ea.com>
> Cc: bldg-sim at lists.onebuilding.org
> Sent: Saturday, May 14, 2011 4:36:22 PM GMT -05:00 US/Canada Eastern
> Subject: RE: [Bldg-sim] Energy Model Cost - best design doesn'tequalmost
> LEED points
>
>
>  The primary purpose is to get the conversation started, early.  It is an
> opportunity to educate the owner and the team about energy.  In my
> experience the majority of designers can’t even tell you the metric for
> comparing building energy consumption.  I have often had this conversation
> early in the project design and have been met with blank stares.  It is
> incumbent upon us who do understand these energy issues to get the
> conversation started.  Caveat the heck out of the goal, explain the
> limitations, discuss the relative vs absolute metrics, be open about the
> issues – so that we can raise awareness one conversation at a time.  This is
> the power of a market transformation tool like LEED.  It enables us to have
> these conversations.
>
>
>
> I agree that both of these items are potential issues, talk to your clients
> about them.  If you don’t have a goal, how do you measure success?
>
>
>
> Marcus Sheffer
>
> Energy Opportunities, Inc/a 7group Company
>
> 1200 E Camping Area Road, Wellsville, PA  17365
>
> 717-292-2636, sheffer at sevengroup.com
>
> www.sevengroup.com
>
>
>
> *From:* Julia Beabout [mailto:juliabeabout at yahoo.com]
> *Sent:* Saturday, May 14, 2011 9:57 AM
> *To:* Marcus Sheffer; Nick Caton; Hussein Abaza; Bill Bishop
> *Cc:* bldg-sim at lists.onebuilding.org
> *Subject:* Re: [Bldg-sim] Energy Model Cost - best design doesn'tequalmost
> LEED points
>
>
>
> While I conceptually agree with and understand the kbtu or watts/sf
> approach, to me, there seems to be some series issues with it in reality.
>
> First, I don't agree that generating or coming up with appropriate target
> values during design is always (or even frequently) an easy thing to do or
> easy data to find.  It depends on your bldg type.  I do a lot of labs and
> hospitals.  Manufacturing and industrial use bldgs can have the same
> issues.  Good EUI data is not easy to come by for these bldg types - partly
> because the user equipment that is installed in them can be a big portion of
> the energy demand and consumption and it's always changing and can be very
> specific to each client.  For example: is it a community hosptial with more
> modest and generic care provide?....a state of the art hospital with
> specialized care functions?....does the lab have primarily biology or a
> chemistry functions....etc etc.  These things all affect the EUI.  In my
> opinion, the best resource for this data is actually utility companies based
> on data from similar customers, but that data is not generally publicly
> available and/or the population of similar comparable buildings may be small
> and difficult to relate to your bldg.
>
> Second, quite frankly, in my opinion, DESIGN phase energy models are poor
> predictors of ACTUAL bldg energy use.  They are best at predicting RELATIVE
> (comparative) energy use.  This is not because the tools are not good or
> inaccurate but because we and the owners are so poor at predicting how the
> bldg will actually be used, weather, etc.  One additional factor, is what
> equipment will actually be installed.  It's not uncommon for the technology
> to have changed bewteen the time that we start design and the time the
> equipment is actually purchased closer to the end of construction.  All
> these things effect not only the equipment w/sf usage but the ac w/sf usage
> etc.   So, there seems to me to be a serious disconnect to me if we talking
> about setting energy targets during DESIGNbased on statistical data of
> ACTUAL energy use and trying to use those figure during the design phase for
> predicted energy use.  Again, I love the idea but are we really there yet in
> reality.  It seems to me we need a lot more data that doesn't exist yet -
> and mechanism to collect that data.  (CBECS etc are good, but the population
> and variability for bldgs of these types has a long way to go).
>
> I missing something about what's being proposed/talked about?
>
>
>
>
>  ------------------------------
>
> *From:* Marcus Sheffer <sheffer at energyopportunities.com>
> *To:* Nick Caton <ncaton at smithboucher.com>; Hussein Abaza <
> ahussein at spsu.edu>; Bill Bishop <wbishop at pathfinder-ea.com>
> *Cc:* bldg-sim at lists.onebuilding.org
> *Sent:* Fri, May 13, 2011 7:01:25 PM
> *Subject:* Re: [Bldg-sim] Energy Model Cost - best design doesn'tequalmost
> LEED points
>
> First of all the goal is not at all arbitrary but must be based on an
> expected outcome within a reasonable expectation.  It is informed by data
> from similar, actual building energy consumption.  I don’t think I need to
> explain the tools one can use to do this.
>
>
>
> Your goal (do the best you can) sounds like, “let’s build an energy
> efficient building”.  This is meaningless.  Energy efficiency in the context
> of new construction is always relative and without a quantification of what
> energy efficient means this is no goal at all.
>
>
>
> Like any early stage performance goal the number is adjustable as more is
> discovered in the design process.  If the target is later discovered to be
> unreasonable due to a wide range of potential issues, then the target is
> adjusted.
>
>
>
> If you pick your EUI goal the way you describe then yes this is a worthless
> goal but the key point is that it is never selected arbitrarily.
>
>
>
> Marcus Sheffer
>
> Energy Opportunities, Inc/a 7group Company
>
> 1200 E Camping Area Road, Wellsville, PA  17365
>
> 717-292-2636, sheffer at sevengroup.com
>
> www.sevengroup.com
>
>
>
> *From:* Nick Caton [mailto:ncaton at smithboucher.com]
> *Sent:* Friday, May 13, 2011 6:17 PM
> *To:* Marcus Sheffer; Hussein Abaza; Bill Bishop
> *Cc:* bldg-sim at lists.onebuilding.org
> *Subject:* RE: [Bldg-sim] Energy Model Cost - best design doesn'tequalmost
> LEED points
>
>
>
> Not to be a jerk, but to ask an honest question: what is the point?  I’ve
> been involved with “established energy target” projects and never really
> picked up on the logic behind it – I would appreciate a layman’s
> explanation.
>
>
>
> Put another way:  If you select an arbitrary EUI or watts per square foot
> at the earliest stages of design, what have you gained in design process?
> If/when a project “meets the goal” mid-design, are future design decisions
> supposed to de-emphasize energy impact (no!)?  If on the other hand, a
> project finds that target unreasonable down the road, what then?
>
>
>
> Not setting a mile-marker like this implies designing the best building you
> can given the time/budget available and any other constraints… that seems
> more likely to result in the best end-result to me.
>
>
>
> To draw analogy, if design of a LEED (or any energy-conscious) project is
> like planning a road trip from Kansas to Florida, setting EUI goals seems
> something like choosing a rest stop by throwing a dart at the map
> blindfolded.  It doesn’t help you get to your destination any more
> efficiently, it may be far out of the way, and now you’ve got a hole in the
> wall… what was the point?
>
>
>
> Okay, maybe a weak analogy – chalking it up to a very long week =).
> Honestly, I’d appreciate someone laying the value behind this approach – I’m
> expect the logic does exist, and I just haven’t yet seen the light!
>
>
>
> ~Nick
>
>
>
> [image: cid:489575314 at 22072009-0ABB]
>
> * *
>
> *NICK CATON, E.I.T.*
>
> PROJECT ENGINEER
>
> Smith & Boucher Engineers
>
> 25501 west valley parkway
>
> olathe ks 66061
>
> direct 913 344.0036
>
> fax 913 345.0617
>
> www.smithboucher.com* *
>
>
>
> *From:* bldg-sim-bounces at lists.onebuilding.org [mailto:
> bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *Marcus Sheffer
> *Sent:* Friday, May 13, 2011 4:36 PM
> *To:* 'Hussein Abaza'; Bill Bishop
> *Cc:* bldg-sim at lists.onebuilding.org
> *Subject:* Re: [Bldg-sim] Energy Model Cost - best design doesn'tequalmost
> LEED points
>
>
>
> Agreed.  The new credit language for the next version of LEED does ask
> project teams to establish an absolute performance goal.
>
>
>
> Marcus Sheffer
>
> Energy Opportunities, Inc/a 7group Company
>
> 1200 E Camping Area Road, Wellsville, PA  17365
>
> 717-292-2636, sheffer at sevengroup.com
>
> www.sevengroup.com
>
>
>
> *From:* bldg-sim-bounces at lists.onebuilding.org [mailto:
> bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *Hussein Abaza
> *Sent:* Friday, May 13, 2011 10:15 AM
> *To:* Bill Bishop
> *Cc:* bldg-sim at lists.onebuilding.org
> *Subject:* Re: [Bldg-sim] Energy Model Cost - best design doesn't
> equalmost LEED points
>
>
>
> Could any one advice why LEED would not put the base design as Watt per
> square foot, or per occupant, or per hotel bed etc. so the Architecture
> becomes more innovative early in the design to save energy?
>
> ----- Original Message -----
> From: "Bill Bishop" <wbishop at pathfinder-ea.com>
> To: "Arpan Bakshi" <arpanbakshi at gmail.com>
> Cc: bldg-sim at lists.onebuilding.org
> Sent: Friday, May 13, 2011 10:11:30 AM GMT -05:00 US/Canada Eastern
> Subject: Re: [Bldg-sim] Energy Model Cost - best design doesn't equal
> most        LEED points
>
> Arpan,
>
>
>
> Based on the Weidt Group paper, I’m guessing you’re emphasizing
> architectural considerations that affect the energy cost vs. LEED points
> numbers. (The paper uses window-to-wall ratios and daylighting as an
> example.) I would think the goal during the programming and schematic design
> phases should be energy cost, not LEED points relative to the App. G
> baseline. Much of the energy cost savings vs. App. G baseline (EAc1 points)
> is going to come later from the mechanical and lighting designs. The
> suggestions in the paper to establish specific baseline building shapes and
> glazing percentages would add a LOT more modeling time – you’d have to
> create two separate building geometries for the baseline and proposed
> models, not to mention different zoning patterns, space types, lighting
> power per space etc.
>
>
>
> For mechanical design, once the size and programming of the project is
> established, the baseline model properties are pretty well set, unless you
> consider fuel-switching and go between baseline systems 1/3/5/7 to systems
> 2/4/6/8. One exception I can think of for a design decision that results in
> higher energy cost but better comparison with the App. G baseline is higher
> ventilation rates combined with heat recovery in the proposed and no heat
> recovery in the baseline.
>
>
>
> Regards,
>
> Bill
>
>
>
> [image: Signature in jpg form]
>
>
>
> *From:* bldg-sim-bounces at lists.onebuilding.org [mailto:
> bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *Arpan Bakshi
> *Sent:* Friday, May 13, 2011 9:09 AM
> *To:* sheffer at energyopportunities.com
> *Cc:* <bldg-sim at lists.onebuilding.org>
> *Subject:* Re: [Bldg-sim] Energy Model Cost
>
>
>
> Marcus, thank you incorporating this language.
>
>
>
> The one scenario we often see in our design guidance work is that a
> proposed design when compared with other design alternates does not
> necessarily provided the largest energy savings when compared against its
> own baseline case model. It is difficult to make a recommendation as
> consultants when we want to present the Owner with both real energy cost
> savings without compromising their LEED certification level targets.
>
> A recent paper presented by the Weidt Group at SimBuild touched on this
> issue:
>
>
>
>
> http://www.ibpsa.us/pub/simbuild2010/technicalPresentations/SB10-PPT-TS02A-03-Baker.pdf
>
>
>
>
>
>
>
> Arpan Bakshi, LEED AP BD+C
>
> YRG sustainability
>
>
> On May 13, 2011, at 8:16 AM, "Marcus Sheffer" <
> sheffer at energyopportunities.com> wrote:
>
>  If anyone has any good ideas about how to structure the LEED credits to
> end the practice of validation models at the end and encourage/require
> design phase modeling the folks on the USGBC EA TAG would love to hear
> them.  The current proposed credit language from the first public comment
> phase is listed below.
>
>
>
> NC, CS, SCHOOLS, RETAIL, WAREHOUSE & DISTRIBUTION CENTERS, HOSPITALITY
>
> Establish an energy performance target no later than the schematic design
> phase. The target must be established as kBTU per square foot-year of source
> energy use. This target must be mapped on the same scale as the baseline and
> proposed buildings, if the project follows Option 1.
>
>
>
> OPTION 1. Whole Building Energy Simulation
>
> Analyze a minimum of at least nine efficiency measures during the design
> process and account for the results in design decision-making. Analysis can
> include energy simulation of efficiency opportunities, application of past
> energy simulation analyses for similar projects to the project, or
> application of published data from energy analyses performed for similar
> projects to the project (such as AEDGs).
>
>
>
> A minimum of six energy efficiency measures focused on load reduction
> strategies appropriate for the facility must be analyzed. This analysis must
> be performed during the schematic design phase.
>
>
>
> A minimum of three energy efficiency measures focused on HVAC related
> strategies must be analyzed (passive measures are acceptable). This analysis
> must be performed before the conclusion of the design development phase.
>
>
>
> The results of the analysis must be summarized in a brief report or
> memorandum.
>
>
>
>
>
> The next version of LEED will be going out for public comment again in
> July, I think, so please comment formally as well as discussing here.
>
>
>
> Marcus Sheffer
>
> Energy Opportunities, Inc/a 7group Company
>
> 1200 E Camping Area Road, Wellsville, PA  17365
>
> 717-292-2636, sheffer at sevengroup.com
>
> www.sevengroup.com
>
>
>
> *From:* John Aulbach [mailto:jra_sac at yahoo.com]
> *Sent:* Thursday, May 12, 2011 7:46 PM
> *To:* Carol Gardner; Marcus Sheffer
> *Cc:* bldg-sim at lists.onebuilding.org
> *Subject:* Re: [Bldg-sim] Energy Model Cost
>
>
>
> OK, Carol..now you threw the "bait" out there..older than dirt, eh?
>
>
>
> I have done very limited LEED "type" modeling where you compare 20 walls
> and 40 windows types (well, it seemed that way). Correct me if I am wrong,
> but a Base model must be built to comply with a certain level of ASHRAE 90.1
> (now up to 2010 ??). With all of the nuisances of eQuest 3.64, I am going to
> build the model from scrathc and put in all the relevant baseline data in by
> hand.  And, by the way, the ASHRAE baseline model might be an entirely
> different system.  I am just completing an EPACT evaluation (ASHRAE
> 90.1-2001) and the Baseline HVAC was screwe chillers, whereas the Actual
> building was packaged units with Turbocor compressors (ask me how I did
> that).
>
>
>
> It very much depends on the complexity of the building. A 40,000 sf office
> or a 500,000 sf hotel with casino facilites.
>
>
>
> I am unfamiliar with the LEED paperwork to be filled out after the modeling
> has been done. But I would not do anything of this type in under 120 hours,
> preferably 160 hours. If the client thinks he can do better, let him.
>
>
>
> Contingency, contingency.
>
>
>
> We won't discuss how old CAROL might be..
>
>
>
> John A.
>
>
>  ------------------------------
>
> *From:* Carol Gardner <cmg750 at gmail.com>
> *To:* sheffer at energyopportunities.com
> *Cc:* bldg-sim at lists.onebuilding.org
> *Sent:* Thu, May 12, 2011 2:59:12 PM
> *Subject:* Re: [Bldg-sim] Energy Model Cost
>
> Marcus,
>
> You have inadvertently hit upon why IBPSA worked with ASHRAE to create a
> BEMP certification. That's Building Energy Modeling Professional (BEMP).
>
> Some of us who have been in the field for awhile began to worry a couple of
> years ago when so many new energy modelers began appearing on the listserv
> with questions. Their questions indicated a lack of training and experience
> that was worrisome. What made it worrisome was that they didn't seem to
> realize that they were as inexperienced as they were; they didn't appear to
> be pursuing training to learn how to do what they were doing; and we were
> uncertain as to how or if they were practicing quality control. We hoped
> that by creating a path to certification that we would give clients one more
> qualification to look for in their modelers.
>
> If you have been in this industry for any length of time, and by industry I
> mean the overall construction industry, you know that you don't get a lot of
> chances if your work doesn't pan out. If your energy model says I have a
> LEED Gold building and I'm going to save $4,000/year and what I really get
> is LEED Silver and $1,000/year, I am not going to be happy. So, I will
> probably not give you any more work but, even worse for all of us, I'll
> start expressing doubts about the whole process. LEED - what is it good for?
>
> So, now we all have more training, right? We read our ASHRAE Handbooks and
> technical manuals so we know how to model the difficult stuff. We can find
> any topic in the DOE2 Manuals, all of which are one line, available, and
> easily searchable.
>
> So now we are so good we can do these models in 40-80 hours. Really? Not me
> and I've been doing it longer than everyone, except you, John Aulbach. So
> I'm going to join Marcus in his rant because he's on to something.
>
> It's up to us to not under bid this work. It's up to us to educate our
> clients about the importance of quality in this process. If they think they
> are getting the same analysis in 40 hours that they used to get in 120
> hours, they need to be led around to rethinking that and to be reminded that
> GIGO.
>
> Cheers,
>
> Carol
>
>
> Thu, May 12, 2011 at 2:31 PM, Marcus Sheffer <
> sheffer at energyopportunities.com> wrote:
>
>  In our experience a final model, done right, would take about 80 hours.
>
>
>
> WARNING – frustrated modeling rant to follow:
>
>
>
> Doing just a final model however completely misses the point as to why we
> model – it is to guide design decisions!
>
>
>
> If I saw this RFP and all it asked me for was a model to determine LEED
> points, during or after design, I would try to educate the potential client
> about the purpose of modeling.
>
>
>
> Unfortunately too many projects pursuing LEED are only doing the minimum
> when it comes to modeling and almost completely missing all the benefits.
> Too often the “market” transforms only based on a least first cost
> denominator basis that results in little real transformation.  Doing models
> to determine LEED points does not transform the market, save any energy, and
> just circumvents the purpose behind LEED. (the next version actually
> requires design phase modeling!)
>
>
>
> Any “modeler” who does only final models without attempting to explain to
> the owner why this is a bad idea should be “drummed out of the corp” in my
> humble opinion.
>
>
>
> The problem is that if you respond to this RFP with 120 or 160 or more
> hours to really do the design phase modeling right, you will go up against
> the “modeler” who claims to be able to do it in far less time.  So how do we
> get the folks who issue the RFPs to ask for a proper scope of work so that
> they can compare fees on a level playing field?  It is unfortunate that we
> are even having a discussion about doing modeling work in opposition to its
> purpose.
>
>
>
> Sorry for the rant but I feel better now. J
>
>
>
> Marcus Sheffer
>
> Energy Opportunities, Inc/a 7group Company
>
> 1200 E Camping Area Road, Wellsville, PA  17365
>
> 717-292-2636, sheffer at sevengroup.com
>
> www.sevengroup.com
>
>
>
> *From:* bldg-sim-bounces at lists.onebuilding.org [mailto:
> bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *Demba Ndiaye
> *Sent:* Thursday, May 12, 2011 4:28 PM
> *To:* Omar Delgado; bldg-sim at lists.onebuilding.org
> *Subject:* Re: [Bldg-sim] Energy Model Cost
>
>
>
> Omar,
>
>
>
> I would expect, for a building this size, approximately 40 hours (multiply
> by your hourly rate). The 40 hours include EAp2/EAc1 LEED documentation, and
> any review you may have to respond to later.
>
>
>
> Now, given that you have never done a LEED model, it will take you more
> time, possibly up to 40 more hours.
>
>
>
> HTH,
>
>
>
> _______________
>
> Demba NDIAYE
>
>
>
> *From:* bldg-sim-bounces at lists.onebuilding.org [mailto:
> bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *Omar Delgado
> *Sent:* Thursday, May 12, 2011 7:08 PM
> *To:* bldg-sim at lists.onebuilding.org
> *Subject:* [Bldg-sim] Energy Model Cost
>
>
>
> Greetings everyone,
>
>
>
> I have a question regarding the cost of an energy model for a LEED project.
> Every energy model I've done so far has been for
>
> existing buildings, mainly for optimization purposes. However, I received
> an RFP to model a five-story, 41,500 sq. ft. building
>
> that's currently on the design phase and is pursuing the LEED-NC Silver
> certification. I really have no idea what would be a fair
>
> price for this model since I'm going to have to use Appendix G (ASHRAE
> 90.1) to evaluate the difference between the base
>
> and proposed buildings. I don't know how much extra effort this will take.
> I know the procedure, just haven't done it before.
>
>
>
> Can you shed any light on this issue?
>
>
>
> Thanks in advance!
>
>
>
> *Omar A. Delgado Colón, P.E., MEnvM., LEED AP BD&C*
>
> *Vice President*
>
> *EnerMech*
>
> PMB 340
>
> 130 Winston Churchill Ave.
>
> San Juan, PR 00926-6018
>
> Cel. (787) 224-6537
>
> odelgado at enermechpr.com
>
> info at enermechpr.com
>
> www.enermechpr.com
>
>
>
>
>
>
>
> <image001.gif> *Please consider your environmental responsibility before
> printing this e-mail*
>
> This Email is covered by the Electronics Communications Privacy Act, 18
> U.S.C. Sections 2510-2521 and is legally priviliged. The information in this
> email is personal and confidential and is intended solely for the
> addressee(s). Access to this email by anyone else is unauthorized. If you
> are not an intended recipient, you must not read, use or disseminate the
> information contained in the email. Any views expressed in this message are
> those of the individual sender and may be subject to Attorney/Client
> privilege and/or Work Product. You are hereby notified that any
> dissemination, distribution or copying of this communications is strictly
> prohibited.
>
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
> --
> Carol Gardner PE
>
>  _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> _______________________________________________ Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org To
> unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
> --
>
> *Dr. Hussein Abaza, Assistant Professor*
>
> *Construction Management Department *
>
> *SCHOOL OF ARCHITECTURE’*
>
> *CIVIL ENGINEERING TECHNOLOGY*
>
> * And CONSTRUCTION*
>
> 1100 South Marietta Parkway, Marietta, GA 30060-2896
>
> Website: www.spsu.edu/cost  Tel: 678-915-3719 Fax: 678-915-4966
>
> E-mail: ahussein at spsu.edu
>
>
>
>
>
>
>
> --
>
> *Dr. Hussein Abaza, Assistant Professor*
>
> *Construction Management Department *
>
> *SCHOOL OF ARCHITECTURE’*
>
> *CIVIL ENGINEERING TECHNOLOGY*
>
> * And CONSTRUCTION*
>
> 1100 South Marietta Parkway, Marietta, GA 30060-2896
>
> Website: www.spsu.edu/cost  Tel: 678-915-3719 Fax: 678-915-4966
>
> E-mail: ahussein at spsu.edu
>
>
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>