[Bldg-sim] centrlized air source heat pump
Chris Jones
cj at enersave.ca
Mon Oct 24 14:09:40 PDT 2011
Maher
The central plant with air source heat pump and possibly boiler
backup (gas/electric) can be modelled using EE4. The EE4 Version
1.70 Modelling Guide provides guidance in Section 4.6.4. The
modelling guide can be downloaded from
http://canmetenergy-canmetenergie.nrcan-rncan.gc.ca/eng/software_tools/ee4/modelling_guide.html
Use the seasonal efficiency of the air source heat pump. The "ground
source" is the heat exchanger. In your case the heat exchanger is the
air. You could be modelling a sea-water source heat-pump with backup
boiler.
The only caveat is that you cannot model a water-source heat pump
HVAC system if you use the Combination Ground Source Heat Pump plant.
At 02:52 PM 21/10/2011, Maher Hemod wrote:
>Content-class: urn:content-classes:message
>Content-Type: multipart/alternative;
> boundary="----_=_NextPart_001_01CC9022.89EEB8B3"
>
>
>
>Hi every one
>any one can help How can I modle centrlized air source heat pump in
>EE4 1.7 (Canadain energy simulation tools )?
>Maher Hemod, EIT
>Design Engineer
>Building Simulation Specialist
>ph. 604.888.7779
><mailto:sabah.ali at rpeng.ca>maher.hemod at rpeng.ca
>
>_______________________________________________
>Bldg-sim mailing list
>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>To unsubscribe from this mailing list send a blank message to
>BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
Chris Jones
14 Oneida Avenue
Toronto, ON M5J 2E3.
Tel. 416-203-7465
Fax. 416-946-1005
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111024/04e0f6ce/attachment-0002.htm>
More information about the Bldg-sim
mailing list