[Bldg-sim] EE4: Boiler/Cooling Tower Set Points, and Max Heating COP
    RobertWichert 
    robert at wichert.org
       
    Thu Apr 12 12:57:05 PDT 2012
    
    
  
Justin,
Do you have any ideas on how to get around having the cooling tower 
setpoint above the boiler setpoint?  This makes no sense to me with a 
cooling tower cooled condenser  and a boiler heated reheat loop.  They 
aren't even connected!
I agree that the limitation is proper for a heat pump, since you don't 
want the boiler just rejecting heat to the cooling tower, but if the two 
loops are not connected (like a hydronic heating system with a water 
cooled condenser DX system) the limitation doesn't make sense.
Robert Wichert P.Eng. LEED AP BD&C
+1 916 966 9060
FAX +1 916 966 9068
===============================================
On 4/12/2012 12:32 PM, Krauel, Danielle wrote:
> Justin,
>
> You can modify the HEATING-EIR (reciprocal of COP) in the DOE code for all zones to achieve the high COP's of a hybrid heat pump (so that you aren't using electricity (compressors) energy for heating).
>
> Kind regards,
> Danielle Krauel P.Eng., LEED AP
> Halsall Associates
> Tel: 613.907.7540 . Toll Free: 1.877.442.5725 x 286 . www.halsall.com
> Vancouver . Calgary . Sudbury  . Burlington . Toronto . Ottawa . Dubai
> Best Workplaces in Canada, Five Consecutive Years: 2007 - 2011
> __________________________
> A Parsons Brinckerhoff Company
>
>
> -----Original Message-----
> From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of bfountain at greensim.com
> Sent: April 12, 2012 3:22 PM
> To: Justin Elkin; bldg-sim-bounces at lists.onebuilding.org; bldg-sim at lists.onebuilding.org
> Subject: Re: [Bldg-sim] EE4: Boiler/Cooling Tower Set Points, and Max Heating COP
>
> 2) Yup - 8 is as high as you can go.
>
> 1) The boiler setpoint (for a heat pump condenser loop) must be lower than the cooling tower setpoint which is set on the cooling tower tab.
> Brian Fountain
> bfountain at greensim.com
>
> -----Original Message-----
> From: Justin Elkin<jelkin at mreng.ca>
> Sender: bldg-sim-bounces at lists.onebuilding.orgDate: Thu, 12 Apr 2012 16:00:14
> To:<bldg-sim at lists.onebuilding.org>
> Subject: [Bldg-sim] EE4: Boiler/Cooling Tower Set Points, and Max Heating COP
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
    
    
More information about the Bldg-sim
mailing list