[Bldg-sim] Baseline System For Semi-Heated Space for LEED
    Bishop, Bill 
    bbishop at pathfinder-ea.com
       
    Fri Aug 17 06:16:27 PDT 2012
    
    
  
Karen,
A "semi-heated" space is not a "conditioned space" per ASHRAE 90.1. For a LEED/Appendix G model, the baseline system type is based on conditioned floor area, and the requirement for modeling heating and cooling applies to conditioned spaces only. You could model the space as unconditioned in the baseline and proposed models, and capture the semi-heating as neutral process energy.
Alternatively, you could use System Type 9 or 10 from ASHRAE 90.1-2010. Systems 9 and 10 apply to "thermal zones designed with heating only systems in the proposed design, serving storage rooms, stairwells, vestibules, electrical/mechanical rooms, and restrooms not exhausting or transferring air from mechanically cooled thermal zones in the proposed design" per G3.1.1 Exception e. The ASHRAE definition for "zone, HVAC" is "a space or group of spaces...", not "a conditioned space...". So I think you could apply System 9 or 10 to a semi-heated space, if the space type is one of those listed.
Either of these options should be easy enough to change/undo if a LEED reviewer disagrees with your approach.
Regards,
Bill
[Senior Energy Engineer 28Jun2012]<mailto:wbishop at pathfinder-ea.com>
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Karen Walkerman
Sent: Thursday, August 16, 2012 8:36 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Baseline System For Semi-Heated Space for LEED
Hi,
I have a space that meets the requirements of a "semi-heated" space.  Question is - how do I model the baseline system?  I have found no information in AppG, LEED, or any other resources.
Thanks,
--
Karen
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120817/9adad095/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 20869 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120817/9adad095/attachment-0002.jpg>
    
    
More information about the Bldg-sim
mailing list