I'm confused by both the original post and the subsequent replies. What does this have to
do with weather data or with eQUEST?
Weather files do not list the ASHRAE climate region. If you got a weather file from the
EERE site, then that's an EnergyPlus EPW weather file. The ASHRAE Climate Zone shown on
an EPW STAT file is calculated by the EnergyPlus weather processor in converting the
source weather file into an EPW. It has no bearing on the weather file itself. If you
think that the Climate Zone is in error, that only means
the algorithm used by the EnergyPlus weather processor to calculate the ASHRAE Climate
Zone may be faulty for international locations.
Referring to this as a bug in eQUEST, or suggesting the problem might be the eQUEST *.BIN
weather file are further off the mark.
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
www.whiteboxtechnologies.com
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 12/3/2012 6:27 AM, Chuck Khuen wrote:
> We are now producing weather files in BIN format for pretty much anywhere outside the US
> at weatheranalytics.com. Not free but simple and quick.
> Chuck
> _________________
> Chuck Khuen
> Co-Founder, EVP
> Weather Analytics
> weatheranalytics.com
> 781-856-5383
>
> *From:* Waseem Shah Khan <mailto:waseem at edsglobal.com>
> *Sent:* Monday, December 03, 2012 1:34 AM
> *To:* bldg-sim at lists.onebuilding.org <mailto:bldg-sim at lists.onebuilding.org>
> *Subject:* Re: [Bldg-sim] Bldg-sim Digest, Vol 60, Issue 21
> Dear Eleni,
>
> I am from india, Same problem with me, there is a bug in eQuest for international
> climate zone. it will only for US.
>
>
> On Sat, Dec 1, 2012 at 2:30 AM, <bldg-sim-request at lists.onebuilding.org
> <mailto:bldg-sim-request at lists.onebuilding.org>> wrote:
>
> Send Bldg-sim mailing list submissions to
> bldg-sim at lists.onebuilding.org <mailto:bldg-sim at lists.onebuilding.org>
>
> To subscribe or unsubscribe via the World Wide Web, visit
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> or, via email, send a message with subject or body 'help' to
> bldg-sim-request at lists.onebuilding.org <mailto:bldg-sim-request at lists.onebuilding.org>
>
> You can reach the person managing the list at
> bldg-sim-owner at lists.onebuilding.org <mailto:bldg-sim-owner at lists.onebuilding.org>
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of Bldg-sim digest..."
>
> Today's Topics:
>
> 1. International Climate Zone specification
> (elenisoulti at co2engineering.eu <mailto:elenisoulti at co2engineering.eu>)
>
>
> ---------- Forwarded message ----------
> From: elenisoulti at co2engineering.eu <mailto:elenisoulti at co2engineering.eu>
> To: "bldg-sim at lists.onebuilding.org <mailto:bldg-sim at lists.onebuilding.org>"
> <bldg-sim at lists.onebuilding.org <mailto:bldg-sim at lists.onebuilding.org>>,
> "equest-users at lists.onebuilding.org <mailto:equest-users at lists.onebuilding.org>"
> <equest-users at lists.onebuilding.org <mailto:equest-users at lists.onebuilding.org>>
> Cc:
> Date: Fri, 30 Nov 2012 20:58:48 +0000
> Subject: [Bldg-sim] International Climate Zone specification
> Dear all,
>
> I am using eQUEST for a project in Spain and I have used the weather data from the
> EERE (Energy Efficiency & Renewable Energy) website. The climate zone described in
> the weather file doesn't seem to agree with the one I calculate according to the
> ASHRAE 90.1 description for International climate zones, based on the precipitation
> levels. Has anyone had any similar problems with weather data outside the US? Any
> suggestions about dealing with this?
>
> Thank you in advance.
>
> Kind regards,
>
> Eleni
>
> --
> Eleni Soulti
>
> On behalf of
>
> CO2 Engineering
>
> Oficina Sevilla
>
> Cartuja - Edificio Marie Curie
>
> C/Leonardo da Vinci 18, Planta1 3ºB
>
> 41092 Sevilla | España
>
> T. (0034) 679883055
> begin_of_the_skype_highlighting (0034)
> 679883055 end_of_the_skype_highlighting
>
> London Office
>
> 17, Bishops Close
>
> E17 9RP London | UK
>
> T. (0044) 7969235926
> begin_of_the_skype_highlighting (0044)
> 7969235926 end_of_the_skype_highlighting
>
> Oficina Huelva.
>
> Plaza Hermanos Costalero nº 2, 6º A
>
> 21001 Huelva | España
>
> T. (0034) 647143558
> begin_of_the_skype_highlighting (0034)
> 647143558 end_of_the_skype_highlighting
>
> w. www.co2engineering.eu <http://www.co2engineering.eu>
>
> e. elenisoulti at co2engineering.eu <mailto:elenisoulti at co2engineering.eu>
>
>
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> Bldg-sim at lists.onebuilding.org <mailto:Bldg-sim at lists.onebuilding.org>
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>
>
>
> --
>
> Kind Regards,
>
>
> /Waseem Shah Khan/
>
> Energy Analyst
> /Environmental Design Solutions Pvt. Ltd. /
>
> www.edsglobal.com <http://www.edsglobal.com/>
>
> *Environmental Design Solutions Pvt. Ltd. [EDS]*
> D - 1/25
> Vasant Vihar
> New Delhi 110057,India
>
> Mob:+91.9999535880
> Tel: +91.11.2614.7085
>
> Fax: +91 11 40568633
>
>
> ------------------------------------------------------------------------------------------
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20121203/f34267fa/attachment-0002.htm>
More information about the Bldg-sim
mailing list