[Bldg-sim] Generating or obtaining Real-Time load profiles?
Jeff Haberl
jhaberl at tamu.edu
Thu Dec 6 18:45:49 PST 2012
Jake,
You'll still have to process the data that is output from the program in a repeatable fashion. Therefore, I'd recommend you look at ASHRAE Research Project RP-1093 "Diversity Factor Toolkit".
It contains a set of spreadsheets that take as input 8760 hourly data and convert it into quartile plots that can then be used to determine such things as weekday or weekend profiles. It also outputs DOE-2, BLAST and EP+ schedules that are representative of the mean profiles generated by the spreadsheet that can be cut-and-pasted into your input command file. Its great for making the 3-D plots as well.
Information about the project can be found in:
1. Abushakra, B., Haberl, J., Claridge, D. 2004. “Overview of Literature on Diversity Factors and Schedules for Energy and Cooling Load Calculations (1093-RP),” ASHRAE Transactions-Research, Vol. 110, Pt. 1 (February), pp. 164-176.
2. Claridge, D., Abushakra, B., Haberl, J. 2003. “Electricity Diversity Profiles for Energy Simulation of Office Buildings (1093-RP),” ASHRAE Transactions-Research, Vol. 110, Pt. 1 (February), pp. 365-377.
Copies of the final report, including the spreadsheet can be obtained from Mike Vaughn, Research Manager at ASHRAE.
Jeff
8=! 8=) :=) 8=) ;=) 8=) 8=( 8=) 8=() 8=) 8=| 8=) :=') 8=)8=?
Jeff S. Haberl, Ph.D.,P.E., FASHRAE..............jhaberl at tamu.edu
Professor............................................................Office Ph: 979-845-6507
Department of Architecture.............................Lab Ph:979-845-6065
Energy Systems Laboratory.............................FAX: 979-862-2457
Texas A&M University.....................................77843-3581
College Station, Texas, USA, 77843..................URL:www.esl.tamu.edu
8=/ 8=) :=) 8=) ;=) 8=) 8=() 8=) :=) 8=) 8=! 8=) 8=? 8=)8=0
________________________________
From: bldg-sim-bounces at lists.onebuilding.org [bldg-sim-bounces at lists.onebuilding.org] on behalf of Michael J Witte [mjwitte at gard.com]
Sent: Thursday, December 06, 2012 8:35 PM
To: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Generating or obtaining Real-Time load profiles?
"Real Time Load Profiles" is a very generic term. Since you mention SmartGrid, I assume you mean electric power use profiles. Timeseries CSV files are a common standard output from EnergyPlus and most tools (nearly all the example files produce some variation of this). A single command in EnergyPlus will produce this directly as a csv file if you set the timestep = 60.
Output:Meter, Electricity:Facility, timestep;
The first column is date/time instead of seconds, but that can easily be converted inside excel. This will give you minute-by-minute electric power consumption. Or maybe I'm misunderstanding the question.
Mike
On 12/6/2012 7:19 PM, jake spuggy wrote:
After trying a number of programs (EnergyPlus, BCTV, etc) I find it amazing that there isn't an easier way to generate "Real Time Load Profiles".
I see that these programs, namely EnergyPlus, can "describe" an load profile of a device.
But I really just want CSV files with these 2 columns:
Time (in seconds), Power (average)
The Smart Grid is about making energy decisions in real-time.
Does anyone know how to make these programs output CSV files for researchers like me?
Your advice?
--Jake
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20121207/0e8ac1a2/attachment-0002.htm>
More information about the Bldg-sim
mailing list