[Bldg-sim] Output Variable for Mass Flow Rate
Jim Dirkes
jim at buildingperformanceteam.com
Wed Feb 1 06:06:52 PST 2012
Dear Sachin,
Try these:
In the IDF:
Output:Variable, Name_dischargeNode, System Node Volume Flow Rate Standard
Density, Timestep;
In an RVI file:
Name_dischargeNode, System Node Volume Flow Rate Standard Density
In both cases "Name_dischargeNode" is the name that you are using for the
PTAC air outlet node.
The Building Performance Team
James V. Dirkes II, P.E., BEMP , LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Sachin Sharma
Sent: Wednesday, February 01, 2012 3:01 AM
To: 'bldg-sim at lists.onebuilding.org'
Subject: [Bldg-sim] Output Variable for Mass Flow Rate
Hi,
Which output variable to look for finding the mass flow rate of PTAC supply
fan, if we autosize the supply air flow rate.
Thanks,
With regards,
Sachin Sharma
M.Tech Energy Engg.
Department of Mechanical Engineering
NIT Jaipur
+91 9983912512
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120201/b3208499/attachment-0002.htm>
More information about the Bldg-sim
mailing list