[Bldg-sim] How to Model Parkade CO2 Levels for Exhaust Requirements
Quitadamo, Bob
bquitadamo at RDKEngineers.com
Tue Nov 27 12:45:58 PST 2012
Hi Donal,
You'll want to control outside air off CO (not CO2) in a parking garage and be sure the controls sequence utilize the correct ppm setpoints. Generally there is a minimum ventilation/exhaust rate to maintain even when CO levels are in check for code compliance.
For modeling the system, a specific ventilation schedule correlating to expected usage of the car garage has worked for me in the past. I would imagine similar schedules for this facility have been created for occupancy and lighting/plug loads.
Regards,
Bob Quitadamo
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Dónal O'Connor
Sent: Tuesday, November 27, 2012 9:55 AM
To: Building Sim Forum
Subject: [Bldg-sim] How to Model Parkade CO2 Levels for Exhaust Requirements
Dear building-sim,
I'm currently working on a LEED NC sports facility with an underground parkade for approximately 200 cars.
The parkade exhaust system (100% OA) turns on if the CO2 levels detected in the parkade exceed a particular threshold. Has anybody modeled such a system? What assumptions can be made for the CO2 profile? As it is in a northern climate, I do not want to overestimate the usage of the system which would skew the heating energy required to heat the OA to the required supply temperature.
Your help is greatly appreciated.