[Bldg-sim] heat pump design in Designbuilder
David Cocking
dave at arrow-energy-solutions.co.uk
Tue Sep 4 23:15:41 PDT 2012
Hi Apeksha,
You can model the basic characteristics of an air-source heat pump in simple
HVAC using UK NCM data. There is a simple HVAC tutorial available on
DesignBuilder's website which describes the basic set-up and features of
simple HVAC. Assuming you want heating-only:
1. Go to the HVAC tab, select 'known HVAC system' and edit the details
as below.
2. Set the system type e.g. central heating using radiators or
underfloor heating etc.
3. In the heating tab set the heat source to heat pump: air source
(note different fuel types available).
4. Input the basic performance parameters in the remaining tabs.
If you have both heating and cooling use the split or multi-split system
type and enter the heating details as above.
Regards,
Dave
David Cocking MSc CEng MCIBSE MEI
Director I M: 07939 353791 I E: dave at arrow-energy-solutions.co.uk
Arrow Energy Solutions Ltd I 1 Sundorne Avenue I Shrewsbury I
SY1 4JW
T: 0870 0427264 I F: 0870 8381398 I www.arrow-energy-solutions.co.uk
<http://www.arrow-energy-solutions.co.uk/>
P Do you need to print this? Be green, read on screen.
Privileged/Confidential information and/or Copyright Material may be
contained in this email. The information and material is intended for the
use of the addressee(s) only. If you are not the addressee or the person
responsible for delivering it to the intended addressee(s), you may not copy
or deliver it to anyone else or use it in any unauthorised manner. To do so
is prohibited and may be unlawful. If you receive this email by mistake,
please advise the sender immediately by replying to the email. Although this
email and attachments are believed to be free of any virus or other defects
which might affect any computer or IT systems into which they are received,
no responsibility is accepted by Arrow Energy Solutions Ltd for any loss or
damage arising in any way from the receipt or use thereof.
Arrow Energy Solutions Ltd Registered in England & Wales, Company
Registration No. 6402543. Standard terms and conditions apply.
From: Gupta, Apeksha [mailto:GuptaA at bre.co.uk]
Sent: 04 September 2012 09:46
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] heat pump design in Designbuilder
Hi All,
I'm trying to model a house in Designbuilder heated through an air-source
heat pump. The output I'm after is only the monthly and annual energy
consumption and heating load. Does anyone know which HVAC template to use
for this. I do have the Designbuilder v3 version that can do detailed HVAC
but I'm not after a detailed heat pump design. Any guidance on how to model
heat pumps in simple/compact HVAC in Designbuilder will be useful.
Many thanks,
Apeksha Gupta
Apeksha Gupta MSc
Renewable Energy KTP Associate
BRE Wales & South West
Ethos, Kings Road,
Swansea- SA1 8AS
T +44 1792 630 109 M +44 (0) 754 894 3314 E <mailto:Guptaa at bre.co.uk>
Guptaa at bre.co.uk W <http://www.bre.co.uk/> www.bre.co.uk
MAP: <http://tinyurl.com/brewales> http://tinyurl.com/brewales
_____
For Green Deal news, information and more details on becoming involved:
visit the BRE Green Deal Website Here
Follow BRE on Twitter: @BREwatford <http://twitter.com/brewatford>
_____
Privileged and confidential information and/or copyright material may be
contained in this e-mail. If you are not the intended addressee you may not
copy or deliver it to anyone else or use it in any unauthorised manner. To
do so is prohibited and may be unlawful. If you have received this e-mail by
mistake, please advise the sender immediately by return e-mail and destroy
all copies. Thank you.
Building Research Establishment Ltd, Registered under number 3319324 in
England and Wales. VAT Registration No GB 689 9499 27 www.bre.co.uk
BRE Global Limited, Registered under number 3548352 in England and Wales.
www.breglobal.com
Building Research Establishment and BRE Global are subsidiaries of the BRE
Trust.
BRE Trust is a company limited by guarantee, Registered under number 3282856
in England and Wales, and registered as a charity in England (no. 1092193)
and in Scotland (no. SC039320). www.bretrust.org.uk
Registered Offices: Bucknalls Lane, Garston, Watford, Hertfordshire WD25 9XX
- Travelling to BRE: see www.bre.co.uk/directions
_____
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120905/f00584cb/attachment-0002.htm>
More information about the Bldg-sim
mailing list