[Bldg-sim] Mixed-Use project with multiple meters - Match Proposed or Reality?
Maria Karpman
maria.karpman at karpmanconsulting.net
Thu Sep 6 06:50:05 PDT 2012
Robby,
Note to G2.4 states that using the actual rates ".allows users to gain
credit for features that yield load management benefits. Where such features
are not present, users can simply use state average unit prices from EIA".
Assigning in-unit cooling to residential meter in the baseline versus
non-residential meter in the proposed design may produce cost savings, but
these savings are not due to load management benefits (i.e. reducing peak
demand or shifting it away from peak periods) and thus should not be
contributing to the performance rating. So it looks pretty clear to me that
you should be using non-residential meter for space cooling in the baseline.
Maria
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Robby Oylear
Sent: Wednesday, September 05, 2012 8:00 PM
To: Bldg-sim
Subject: [Bldg-sim] Mixed-Use project with multiple meters - Match Proposed
or Reality?
I have a multifamily project which will have a noresidential electricity
meter to cover house loads and a residential electrical meter for each unit.
The baseline system is System 2 - PTHP's. The proposed system is Chilled
Water with Electric Heat. Due to the rate structures out here in Seattle,
I'm noticing that the virtual rate in the baseline is approximately 10%
higher than in the proposed. I've tracked it down mainly to the fact that
the baseline "Space Cooling" usage is allocated to the Residential meters
while the Proposed "Space Cooling" is provided by a chiller that will be on
a nonresidential meter. In reality, a terminal piece of equipment within a
residence would be metered by the residential panel and charged direct to
the residence. However, it seems a bit unfair that the baseline is being
penalized strictly based on which meter the "Space Cooling" is assigned to.
I can't find anything specifically within Appendix G that would tell me to
have the same energy meters or rate structure by system. The LEED Reference
Guide provides guidance that says the same rate schedules shall be used for
the proposed and baseline simulations and building.
Mixed-use buildings seem to be a weak point of Appendix G and I'm wondering
if anyone else has run into this issue before.
Thanks,
Robby Oylear, PE, LEED AP
Mechanical Engineer
Senior Energy Analyst
D 206-788-4571
www.rushingco.com
_____
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2197 / Virus Database: 2437/5250 - Release Date: 09/05/12
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120906/b6ce4f0a/attachment-0002.htm>
More information about the Bldg-sim
mailing list