[Bldg-sim] Creating a weather file
Joe Huang
yjhuang at whiteboxtechnologies.com
Thu Sep 13 13:57:37 PDT 2012
Since this thread is still bouncing around BLDG-SIM, I thought I'd update others on what I
have done using the ISH data base and sent to Khristiam.
As Krista mentions, the ISH contains two locations : Ciudad Bolivar (WMO 804440) and
General Manuel Carl (WMO 804463). Unfortunately, the second station contains only wind
data and no temperatures, except for half a year in 2011.
The first station, however, contains fairly complete data (~4000 records /year for 2010),
so I processed that to create a usable weather file in the DOE-2 *.BINM format needed for
eQUEST (my procedure also produces other formats such as TMY3, TMY2, and EPW). However,
when Khristiam used the file, it produced significantly lower cooling loads than using
Caracas, which of course doesn't make too much sense. So, I investigated and found that
the weather file I produced contained very low dew point temperatures around 0 C during
many of the nighttime hours. I traced this to the raw ISH data where the station
(airport) had entered +0000 dew point temperatures over 400 times instead of +9999 for
missing data. So, I edited the raw data file and created a corrected weather file, and
made a mental note to modify my procedure to check for such occurences.
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
www.whiteboxtechnologies.com
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 9/13/2012 1:28 PM, Raines, Krista wrote:
> Dear Khristiam,
>
> We use Meteonorm software when we need a weather file for a city that is not in the Energy Plus database. It uses a large weather station database and where there aren't weather stations, the software interpolates data between different stations. The software isn't free though, it's about 500 euros.
> http://meteonorm.com/
>
> Another source I've used that is free or cheap depending on the type of weather data you require is the NOAA site. It looks like their 2 nearest weather stations are called Ciudad Bolivar (Lat: 8.15 deg., Long: -63.550 deg.) and General Manuel Carl (lat: 8.283 deg, long: -62.75 deg.) Here is their site: http://www.ncdc.noaa.gov/cdo-web/#t=firstTabLink. You can search for the stations on the map and get hourly data text files. Usually I take these and convert them to .wea or .epa files through Weather Tool (this is an Autodesk product). You might also be able to use the Energy Plus Weather File Convertor which is free, but I haven't used it to convert text files to weather files before.
>
> Krista Raines, LEED AP BD+C
>
> Kohn Pedersen Fox Associates PC
> 11 West 42nd Street
> New York, NY 10036
> 212 237 3597 (Direct)
> 212 977 6500 (Main)
> 212 956 2526 (Fax)
> www.kpf.com
>
>
>
> -----Original Message-----
> From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Khristiam Alvarez
> Sent: Wednesday, September 12, 2012 8:41 AM
> To: bldg-sim at lists.onebuilding.org
> Subject: [Bldg-sim] Creating a weather file
>
> Hi there
>
> Have anyone experience in creating a new weather file from wunderground data?
>
> This is my case: I use the Caracas file download from the EnergyPlus site converted to eQuest format but I live in other hotter city, Puerto Ordaz that has a wunderground station working since last april.
>
> Thank you very much!
>
> --
> Khristiam Alvarez
> Ingeniero Mecánico
>
> Proyecto Hidroeléctrico Tocoma, Módulo 4 Proyectos Mecánicos Estudios e Ingeniería de Expansión CORPOELEC Km. 85 Vía Guri, Mun. Angostura, Edo. Bolivar, VENEZUELA
>
> Tlfs: 0286.965.3579 / 0424.9701025 / 0416.5861057 Para llamar desde fuera de Venezuela:
> +58.286.9653579 / +58.424.9701025 / +58.416.5861057
>
> "Este contenido es confidencial y de interes exclusivo para el Ministerio del Poder Popular para la Energia Electrica (MPPEE) y sus entes adscritos, por lo tanto, se permite copiar o distribuir el mismo solo a personas autorizadas. Si recibe este correo por error, por favor destruyalo y notifique al remitente. Eventualmente, los correos pueden ser interceptados o alterados, llegar con demora o incompletos, al respecto el MPPEE y sus entes adscritos no se hacen responsables por los errores, defectos u omisiones que pudieran afectar al mensaje original."
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
> -----Original Message-----
> From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of bldg-sim-request at lists.onebuilding.org
> Sent: Thursday, September 13, 2012 4:01 PM
> To: bldg-sim at lists.onebuilding.org
> Subject: Bldg-sim Digest, Vol 58, Issue 9
>
> Send Bldg-sim mailing list submissions to
> bldg-sim at lists.onebuilding.org
>
> To subscribe or unsubscribe via the World Wide Web, visit
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> or, via email, send a message with subject or body 'help' to
> bldg-sim-request at lists.onebuilding.org
>
> You can reach the person managing the list at
> bldg-sim-owner at lists.onebuilding.org
>
> When replying, please edit your Subject line so it is more specific than "Re: Contents of Bldg-sim digest..."
>
> This e-mail transmission is intended only for the use of the individual or entity named above and may contain information that is confidential, privileged, and/or exempt from disclosure under applicable law. If you are not the intended recipient, you are hereby notified that any review, disclosure, copying, distribution, or other use of any of the information contained in this transmission is strictly prohibited. If you have received this transmission in error, please immediately notify the sender by e-mail at the above address and delete it from your computer system; you should not copy the message or disclose its contents to anyone. The content of the message and or attachments may not reflect the view and opinions of the originating company or any party it is representing.
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
More information about the Bldg-sim
mailing list