Hey Jim,
I think you are right.
0.3 x CFM = W
0.3 x (L/S) /0.472 = W
thus
0.636 x L/S = W
Thanks,
Marcin
Marcin Polak, LEED AP BD+C
Energy Engineer
Viridian Energy & Environmental
A Vidaris Company
T: 212.689.5389 x213
mpolak at viridianee.com
www.vidaris.com  www.viridianee.com
________________________________
From: Jim Dirkes [jim at buildingperformanceteam.com]
Sent: Friday, April 26, 2013 1:54 PM
To: EnergyPlus_Support at yahoogroups.com; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Apparent error on ASHRAE 90.1-2007 (and perhaps 2010)
Forgot to say:
A factor of .636 seems to work better.
(SI): (1 L/s * 1000) * .636 = 636 W (This is 1 m3/s)
(IP): 2118.64 cfm * .3  = 636 W  (This is also 1 m3/s)
James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com<http://www.buildingperformanceteam.com/>
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653
From: EnergyPlus_Support at yahoogroups.com [mailto:EnergyPlus_Support at yahoogroups.com] On Behalf Of Jim Dirkes
Sent: Friday, April 26, 2013 1:53 PM
To: EnergyPlus_Support at yahoogroups.com; bldg-sim at lists.onebuilding.org
Subject: [EnergyPlus_Support] RE: Apparent error on ASHRAE 90.1-2007 (and perhaps 2010)
Fabiano,
It?s encouraging that they noticed something, however I don?t think the math works properly with the formula you sent.
(SI): (1 L/s * 1000) * .14 = 140 W (This is 1 m3/s)
(IP): 2118.64 cfm * .3  = 636 W  (This is also 1 m3/s)
James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com<http://www.buildingperformanceteam.com/>
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653
From: EnergyPlus_Support at yahoogroups.com<mailto:EnergyPlus_Support at yahoogroups.com> [mailto:EnergyPlus_Support at yahoogroups.com] On Behalf Of Fabiano Domingues Ferreira
Sent: Friday, April 26, 2013 1:48 PM
To: EnergyPlus_Support at yahoogroups.com<mailto:EnergyPlus_Support at yahoogroups.com>; bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: [EnergyPlus_Support] RES: Apparent error on ASHRAE 90.1-2007 (and perhaps 2010)
Hi Jim,
I was checking 90.1-2010 ? User?s Manual and seems that they have fixed this mistake, follow bellow.
[cid:image001.jpg at 01CE4285.A371A260]
Thanks,
Fabiano Ferreira
De: EnergyPlus_Support at yahoogroups.com<mailto:EnergyPlus_Support at yahoogroups.com> [mailto:EnergyPlus_Support at yahoogroups.com] Em nome de Jim Dirkes
Enviada em: Friday, April 26, 2013 8:11 AM
Para: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>; EnergyPlus_Support at yahoogroups.com<mailto:EnergyPlus_Support at yahoogroups.com>
Assunto: [EnergyPlus_Support] FW: Apparent error on ASHRAE 90.1-2007 (and perhaps 2010)
Dear forums,
I think I have discovered an error in the SI version of ASHRAE 90.1 regarding fan power for Baseline Systems 1 & 2.  I sent the message below to ASHRAE, but then thought, ?Perhaps someone else has also noticed this and received some guidance from ASHRAE?.  Regardless, if it is actually an error, it?s worth mentioning to all of you so that you can be aware of it.
Please  let me know if you are aware of this, and how you have dealt with the discrepancy.  My plan is to use the IP formula because it allows more fan power :).
James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com<http://www.buildingperformanceteam.com/>
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653
From: Jim Dirkes
Sent: Friday, April 26, 2013 5:59 AM
To: 'change.proposal at ashrae.org'
Cc: Santiago Velez (santiago at zondae.com<mailto:santiago at zondae.com>); francisco at zondae.com<mailto:francisco at zondae.com>; 'Jason Glazer'
Subject: Apparent error on ASHRAE 90.1-2007 (and perhaps 2010)
Dear ASHRAE,
I am comparing Appendix G fan power calculations for ASHRAE 90.1 in both SI and IP units.  It appears that they do not agree for Baseline Systems 1 & 2.
The formulae for Systems 1 & 2 are:
(IP): Pfan (watts) = CFMs (cfm) * 0.3
(SI): Pfan (watts) = CFMs (L/s) * 0.3
Calculating fan power for Systems 1&2:
Given:
L/s * 1000 = m3/s
m3/s * 2118.64 = cfm
Substituting these into the fan power equations for Baseline Systems 1 & 2:
(SI): (1 L/s * 1000) * .3 = 300 W
(IP): 2118.64 cfm * .3  = 636 W
The fan power should be identical, but isn?t even close! Have you ever noticed this?  I could not find an errata sheet that corrected the formula. Will you please check to see if there is a correction?  Please make a correction if I am not missing something!
Thank you!
p.s., In a smaller way, the fan power calculations do not agree for the other System types.  This appears to be due in part to using 5 digit precision for IP units and 4 digits for SI (e.g., 0.00094 for IP and 0.0015 for SI)  If you use SI factors of 0.0014857 and 0.0020547 for Systems 3-4 and 5-8 respectively, the agreement is better.
James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com<http://www.buildingperformanceteam.com/>
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653
The information contained in this communication is confidential, may be privileged and is intended for the exclusive use of the above named addressee(s). If you are not the intended recipient(s), you are expressly prohibited from copying, distributing, disseminating, or in any other way using any information contained within this communication. If you have received this communication in error please contact the sender by telephone or by response via mail.
We have taken precautions to minimize the risk of transmitting software viruses, but we advise you to carry out your own virus checks on any attachment to this message. We cannot accept liability for any loss or damage caused by software viruses.
__._,_.___
Reply via web post<http://groups.yahoo.com/group/EnergyPlus_Support/post;_ylc=X3oDMTJxcmZ1cmJqBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BG1zZ0lkAzI4ODY0BHNlYwNmdHIEc2xrA3JwbHkEc3RpbWUDMTM2Njk5ODc3Nw--?act=reply&messageNum=28864>
Reply to sender <mailto:jim at buildingperformanceteam.com?subject=RE%3A%20Apparent%20error%20on%20ASHRAE%2090%2E1-2007%20%28and%20perhaps%202010%29>
Reply to group <mailto:EnergyPlus_Support at yahoogroups.com?subject=RE%3A%20Apparent%20error%20on%20ASHRAE%2090%2E1-2007%20%28and%20perhaps%202010%29>
Start a New Topic<http://groups.yahoo.com/group/EnergyPlus_Support/post;_ylc=X3oDMTJlNGtvcGxuBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA250cGMEc3RpbWUDMTM2Njk5ODc3Nw-->
Messages in this topic<http://groups.yahoo.com/group/EnergyPlus_Support/message/28860;_ylc=X3oDMTM2MjBiYnJhBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BG1zZ0lkAzI4ODY0BHNlYwNmdHIEc2xrA3Z0cGMEc3RpbWUDMTM2Njk5ODc3NwR0cGNJZAMyODg2MA--> (4)
Recent Activity:
?         New Members<http://groups.yahoo.com/group/EnergyPlus_Support/members;_ylc=X3oDMTJmdmx2ZHFoBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzEzNjY5OTg3Nzc-?o=6> 11
Visit Your Group<http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJlcDM5cWFoBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTM2Njk5ODc3Nw-->
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support at gard.com<mailto:energyplus-support at gard.com>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.
EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
MARKETPLACE
________________________________
________________________________
[Yahoo! Groups]<http://groups.yahoo.com/;_ylc=X3oDMTJkZ3BhNDN0BF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxMzY2OTk4Nzc3>
Switch to: Text-Only<mailto:EnergyPlus_Support-traditional at yahoogroups.com?subject=Change%20Delivery%20Format:%20Traditional>, Daily Digest<mailto:EnergyPlus_Support-digest at yahoogroups.com?subject=Email%20Delivery:%20Digest> ? Unsubscribe<mailto:EnergyPlus_Support-unsubscribe at yahoogroups.com?subject=Unsubscribe> ? Terms of Use<http://docs.yahoo.com/info/terms/> ? Send us Feedback <mailto:ygroupsnotifications at yahoogroups.com?subject=Feedback%20on%20the%20redesigned%20individual%20mail%20v1>
.
__,_._,___
This e-mail may contain confidential, copyright or privileged information.  
If you are not the intended recipient or if you have received this e-mail 
in error, please notify the sender immediately and destroy this e-mail.  
Any unauthorized copying, disclosure or distribution of the material in 
this e-mail is strictly forbidden.
Vidaris Inc. cannot guarantee the integrity of this communication.  As the 
Internet is not a guaranteed secure environment, Vidaris Inc. cannot ensure 
that an e-mail is not interfered with during transmission, as such will not 
be held responsible for any damage from e-mail transmission.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130426/ea19c460/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 33255 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130426/ea19c460/attachment-0002.jpg>
    
    
More information about the Bldg-sim
mailing list