[Bldg-sim] warehouse ventilation design
Genest, Frederic
fgenest at pageaumorel.com
Sat Aug 10 14:19:34 PDT 2013
Ramana, code minimum is code minimum, no working around that.
0.06 cfm/ft2 is the right value for warehouse. And it is not CO2 dependant, such sensors do bot apply in those case. Why ventilation is required is to vent out pollutants emitted by the stored goods.
Office space May benefit from sensors, but that is not recommended for spaces with population density < 25 #/1000ft2.
At first reading, your consultants are reading correctly ASHRAE 62.1-2004 (or later). Keep trusting them.
Regards,
Frédéric Genest, ing., associé
Envoyé à partir de mon Windows Phone
________________________________
De : Ramana Koti
Envoyé : 2013-08-09 16:49
À : Bldg-Sim
Objet : [Bldg-sim] warehouse ventilation design
Dear All,
On a large warehouse (shipping & distribution center) project, we're told by our consultant that the 650,000 square feet warehouse component is being designed to be ventilated (OA) at 0.06 cfm/sf. There are small portions with multiple levels, total ventilation CFM ends up being close to 60,000. (we're told by our consultant that this is the code minimum). CO2 sensors are being planned to bring the OA levels down, not yet sure what the thresholds are.
The office component that is a tenth in square footage but roughly equal occupancy as the warehouse, results in around 15,000 CFM ventilation.
While we generally trust our consultant's professional judgement, the design team is concerned that the warehouse ventilation might be over designed. Is anyone aware of workarounds that meet code but effectively optimize the ventilation/OA rates in such large warehouse settings?
Thank you,
Ramana Koti.