[Bldg-sim] ASHRAE 90.1 baseline HVAC sytem description

Duggin, Cory Cory.Duggin at tlc-eng.com
Wed Dec 11 07:19:29 PST 2013


Yes, for ASHRAE 90.1-2007 and 2010 you will have 15 separate VAV AHUs (one per floor) in the baseline.  I'm not sure of the reasoning for the change unless it is simply for standardization of the number of baseline systems.

Cory Duggin, EI
Energy Engineer I
direct: 615-346-1939



From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Linda Lam
Sent: Wednesday, December 11, 2013 9:14 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] ASHRAE 90.1 baseline HVAC sytem description

All,

Can anyone share their experience with the modified baseline model HVAC description in ASHRAE 90.1 - 2007 and 2010? (copied below)  ASHRAE 90.1-2004 did not require the baseline model for systems 5,6,7 and 8 to have separate HVAC systems per floor and I'd like to hear how people have interpreted this and, if anyone can explain the reasoning for this.

For example, the proposed model of a 15 story office building might have 2 AHUs, one serving the east wing and one serving the west wing.  For the baseline per ASHRAE 90.1-2007 or 2010, will these 2 AHUs be replaced with 15 separate VAV units? Or can the 2 AHUs be kept as long as it satisfies the statement "Floors with identical thermal blocks can be grouped for modeling purposes"?

ASHRAE 90.1 - 2004
G3.1.1 Baseline HVAC System Type and Description.
HVAC systems in the baseline building design shall be based
on usage, number of floors, conditioned floor area, and heating
source as specified in Table G3.1.1A and shall conform
with the system descriptions in Table G3.1.1B.

ASHRAE 90.1 - 2007 and 2010
G3.1.1 Baseline HVAC System Type and Description.
HVAC systems in the baseline building design shall be based
on usage, number of floors, conditioned floor area, and heating
source as specified in Table G3.1.1A and shall conform
with the system descriptions in Table G3.1.1B. For systems 1,
2, 3, and 4, each thermal block shall be modeled with its own
HVAC system. For systems 5, 6, 7, and 8, each floor shall be
modeled with a separate HVAC system.  Floors with identical
thermal blocks can be grouped for modeling purposes.

Thanks!

Linda Lam
212 219 2255 | lam at transsolar.com<mailto:lam at transsolar.com>
Transsolar Inc. | 134 Spring St. Suite 601 | New York, NY 10012

Transsolar Climate Engineering
Technical consulting for energy efficiency and environmental quality in buildings
New York - Stuttgart - Munich - Paris

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20131211/d26e4ea6/attachment-0002.htm>


More information about the Bldg-sim mailing list