[Bldg-sim] Appendix G Secondary Pump Control
Nick Caton
ncaton at smithboucher.com
Fri Dec 20 11:43:06 PST 2013
Big Brother GBCI has eyes and ears everywhere... =)
I for one am very happy for clearer direction coming about on this point. For reference, I think that same recent conversation brought about a reference I kept note of for ASHRAE interpretation IC 90.1-2007-14, which ruled that 22 W/GPM is a "whole system" power requirement, similar to Pfan for baseline fan calculations.
The one-third / two-thirds split is to my knowledge new direction, (I have previously simply dumped it all baseline pumping power onto secondary pump for simplicity of documentation - perhaps to my own detriment in certain cases), but I can empathize the reasoning behind providing such direction where distribution of pumping power could (in some cases) affect overall baseline performance.
Thanks very much for sharing James!
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of James Hansen
Sent: Friday, December 20, 2013 11:11 AM
To: Christian Kaltreider; Bishop, Bill; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Appendix G Secondary Pump Control
To clarify an email I sent to the last thread on the 22 W / gpm: I recently received the updated documentation spreadsheet for a v4 pilot project, and they have updated the notes. Not sure if this image will come thru to everybody, so here's what it says:
"The sum of primary and secondary must be 22 W / gpm (349 KW/1000 L/s) per G3.1.3.10. Recommended that the pump power be split as one third (primary) and two-thirds (secondary)."
[cid:image002.png at 01CEFD77.08C09F20]
GHT Limited
James Hansen, PE, LEED AP, BEMP
Senior Associate
1110 N. Glebe Road, Suite 300
Arlington, VA 22201
703.243.1200 (main)
703.338.5754 (direct/cell)
www.ghtltd.com<http://www.ghtltd.com>
From: bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Christian Kaltreider
Sent: Friday, December 20, 2013 11:58 AM
To: 'Bishop, Bill'; bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] Appendix G Secondary Pump Control
Bill,
Thanks. Yes, the 22W/gpm total requirement is still fresh in my mind from the recent discussion on this forum!
I understand your approach to pump control. But...would you be able to defend that approach if someone (like your client) pushed you about why you aren't getting them better savings by running your secondary CHW pump 8760? Certainly the 90.1 folks had some specific intent, whether they made it clear or not...
Thanks,
Christian
From: Bishop, Bill [mailto:bbishop at pathfinder-ea.com]
Sent: Friday, December 20, 2013 10:08 AM
To: Christian Kaltreider; bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: RE: [Bldg-sim] Appendix G Secondary Pump Control
Christian,
I always model one secondary pump for the baseline. I see no reason to do otherwise.
My approach to loop activation has been to model it the same as the proposed design. Using DOE-2 for example, it could be SCHEDULED to run 24/7 during cooling months, or DEMAND-ONLY to stay off until a coil or process load exists. If the proposed design has no CHW plant, but has a boiler/HHW plant, you could model the baseline CHW loop activation similarly to the proposed HHW loop. If the proposed design has no analogous loop operation, you just have to make a judgement call, but I am not aware of any guidance in 90.1 or LEED. Also keep in mind that 22W/gpm is the total pump power allowance for all your primary/secondary CHW pumps, and not the power of each pump.
Regards,
Bill
William Bishop, PE, BEMP, BEAP, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[webCertified_logo_colorRGB72DPI.jpg]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 325-6004 Ext. 114 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
P Sustainability - the forest AND the trees. P
From: bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Christian Kaltreider
Sent: Friday, December 20, 2013 9:15 AM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] Appendix G Secondary Pump Control
I have a question regarding 90.1 2004 Appendix G baseline chilled water pump control. Section 3.1.3.10 says that baseline CHW systems must be primary/secondary, with a constant flow primary loop and a variable flow secondary loop. The secondary pump will either ride the curve or be controlled by a VSD depending on square footage. In the case I currently have in my hands, the pump rides the curve. No questions yet.
Section 3.1.3.11 goes on to state that each chiller shall have its own condenser water and chilled water pumps, interlocked to operate with the chiller. This is clear and reasonable for the condenser water and primary chilled water pumps, but what about secondary chilled water pumps? For my current application (one chiller, pump riding curve), my question simply boils down to whether I should turn the secondary pump off when the chiller is off, or if I should run it all of the time.
But to get into it a little more, here are three approaches I see:
1. Model one secondary pump for each chiller, and turn each pump off when its associated chiller turns off. Section 3.1.3.10 is titled Chilled Water Pumps, and that section includes both primary and secondary pumps, so when the next section references "chilled water pumps" that should include both primary and secondary. However, this does not reflect the typical reality of one secondary pump serving multiple chillers, and the common interpretation that only a primary pump has one single associated chiller.
2. Model one secondary pump regardless of how many chillers there are, and turn it off when all chillers are off. This is perhaps most similar to what you might expect in a 'real' system. If you only have one chiller (as I currently have), this is exactly the same as approach 1.
3. Model one secondary pump regardless of how many chillers there are, and never turn it off. Many buildings are unfortunately operated this way. This approach significantly increases baseline energy when the pump is riding the curve.
I have always used approach 2 without putting much thought into it. But now my results are highly dependent on which approach I take, and I see enough ambiguity that arguments could be made for approach 3.
Your thoughts?
Thanks,
Christian
Christian Kaltreider, LEED AP | Energy Analyst
Sud Associates, P.A. | T 828.255.4691 | F 828.255.4949 | www.sudassociates.com<http://www.sudassociates.com>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20131220/dbafd9b4/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20131220/dbafd9b4/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 42082 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20131220/dbafd9b4/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 3124 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20131220/dbafd9b4/attachment-0005.jpg>
More information about the Bldg-sim
mailing list