[Bldg-sim] Modeling Laboratory DCV and ASHRAE 62?
James Hansen
JHANSEN at ghtltd.com
Wed Feb 6 07:38:53 PST 2013
Thanks for the replies everyone!
I forgot to mention that this is a LEED v4 project, and the verbiage in
90.1-2010 has changed a little bit.
With lab exhaust systems > 5,000 CFM (which ours has), you have to
either have a 50% effective heat recovery device, or the ability to
throttle back non-regulated zones to 50% of the exhaust / makeup air
when not used (there i a fancy equation if you want to combine partial
heat recovery and partial flow reduction). I think you also have the
option to provide direct makeup air that is simply tempered to within a
few degrees of the space setpoint.
So I guess this answers the question for me - I'll end up modeling DCV
for both the proposed and baseline (to 50% of peak ACH for baseline, and
whatever we decide for the proposed), along with heat recovery for the
proposed. I won't have to bring the OA for the baseline all the way
down to ASHRAE 62 values per G3.1.2.11 and 6.5.6.1/6.5.7.2. The other
option is to model 100% full ACH flow for the baseline system along with
a 50% effective heat recovery device, and see if that is more/less
efficient than the other baseline option.
Since G3.1.2.11 in 90.1-2010 now references Section 6, and 6.5.6.1
references 6.5.7.2 which gives multiple options for compliance, it
sounds like there are multiple baseline options for laboratory systems
with exhaust > 5,000 CFM in the new LEED v4.
I wonder if GBCI will provide a ruling on this to clarify down the
road...
GHT Limited
James Hansen, P.E., LEED AP
Senior Associate
1010 N. Glebe Road, Suite 200
Arlington, VA 22201-4749
703-243-1200 (office)
703-338-5754 (cell)
703-276-1376 (fax)
www.ghtltd.com <http://www.ghtltd.com/>
eline
From: Sami, Vikram [mailto:Vikram.Sami at perkinswill.com]
Sent: Tuesday, February 05, 2013 5:07 PM
To: Bishop, Bill; James Hansen; Building SimForum
Subject: RE: Modeling Laboratory DCV and ASHRAE 62?
Also - when you switch from a standard VAV system to a chilled beam
system in a heat gain driven lab there is some reduction. For instance
if your EHS mandated ACH is 6ACH, and thermal loads require you to go up
to 8ACH to meet the cooling needs, that 8ACH has to be 100% OA (sine you
cannot return lab air). A Chilled beam system would allow you to hold
the air changes at 6ACH.
Vikram Sami, LEED AP BD+C
Sustainable Design Analyst
1315 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462 f: 404.892.5823 e: vikram.sami at perkinswill.com
www.perkinswill.com <http://www.perkinswill.com/>
Perkins+Will. Ideas + buildings that honor the broader goals of society
From: bldg-sim-bounces at lists.onebuilding.org [
mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill
Sent: Monday, February 04, 2013 4:05 PM
To: James Hansen; Building SimForum
Subject: Re: [Bldg-sim] Modeling Laboratory DCV and ASHRAE 62?
James,
See this thread for some background on the subject:
http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/2011
-October/010327.html
Most likely, you are correct in thinking that you will have to model the
Baseline with ASHRAE minimum requirements if you model the Proposed with
DCV. Potentially, you could justify modeling the baseline using a local
(or campus?) OA requirement if it is more stringent that ASHRAE 62.1.
If you keep the OA requirement identical between the baseline and
proposed models, there are still opportunities for energy savings:
? from energy recovery (if it is not required in the Baseline
per G3.1.2.10)
? from increased baseline fan power due to pressure drop
adjustments (Return and/or exhaust airflow control devices, others in
Table 6.5.3.1.1B)
? from VAV hoods (this is trickier, but if the baseline system
type is not variable, such as System 3 or 4 per G3.1.1 exception c., the
baseline flow might be autosized at a higher CFM that the proposed
design, and will not be 100% OA. If you model a reduced OA requirement
at night, which is typical and also required in G3.1.1 exception d., the
baseline will still have to run at 100% design flow but with a lower
OA%, while the proposed model can ramp down to save fan energy.)
Regards,
Bill
<mailto:wbishop at pathfinder-ea.com>
From: bldg-sim-bounces at lists.onebuilding.org [
mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of James Hansen
Sent: Monday, February 04, 2013 3:20 PM
To: Building SimForum
Subject: Re: [Bldg-sim] Modeling Laboratory DCV and ASHRAE 62?
Sorry, that last sentence didn't make any sense (thanks Bill). Should
read:
We have a client that wants a specific ACH rate (100% OA, once-thru
system) that is well above the ASHRAE 62.1 OA requirements for
laboratory space in Table 6-1. We would like to use VAV hoods,
occupancy-based exhaust modulation, etc. But since this is considered
DCV, is GBCI really going to require us to bring the lab OA volume down
to ASHRAE 62.1 minimum requirements for the baseline model? Or will we
be allowed to set the baseline OA flow for the laboratory at the minimum
prescribed rates (say 8 ACH), and take credit for flow reduction in the
proposed system?
GHT Limited
James Hansen, P.E., LEED AP
Senior Associate
1010 N. Glebe Road, Suite 200
Arlington, VA 22201-4749
703-243-1200 (office)
703-338-5754 (cell)
703-276-1376 (fax)
www.ghtltd.com <http://www.ghtltd.com/>
From: James Hansen
Sent: Monday, February 04, 2013 3:06 PM
To: Building SimForum
Subject: Modeling Laboratory DCV and ASHRAE 62?
Hi All,
Does anyone have clarity on modeling OA flow rates in laboratory spaces,
specifically how they relate to the LEED baseline requirement for OA
flow when the proposed model has DCV?
We have a client that wants a specific ACH rate (100% OA, once-thru
system) that is well above the ASHRAE 62.1 OA requirements for
laboratory space in Table 6-1. We would like to use VAV hoods,
occupancy-based exhaust modulation, etc. But since this is considered
DCV, is GBCI really going to require us to bring the lab OA volume(flow
reduction) in the proposed system?
Thanks for any advice!
GHT Limited
James Hansen, P.E., LEED AP
Senior Associate
1010 N. Glebe Road, Suite 200
Arlington, VA 22201-4749
703-243-1200 (office)
703-338-5754 (cell)
703-276-1376 (fax)
www.ghtltd.com <http://www.ghtltd.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130206/f0ba0492/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 20869 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130206/f0ba0492/attachment-0002.jpeg>
More information about the Bldg-sim
mailing list