[Bldg-sim] Fan Power
RobertWichert
robert at wichert.org
Fri Feb 22 17:06:46 PST 2013
A 50% efficient MOTOR cannot be correct. 50% efficient fan, yes.
I actually think a lot of the amps given are something akin to MCA.
Let's see what others say...
Robert P. Wichert P.Eng. LEED AP BD&C
+1 916 966 9060
FAX +1 916 966 9068
On Feb 22, 2013, at 1:51 PM, Aaron Smith <asmith at mreng.ca> wrote:
> Robert,
>
> I’ve also run into problems obtaining combined (fan and motor) efficiency and input power, mostly with terminal units such as heat pumps and fan coil units but also with individual fans. What I’ve often done is used the watts listed in their electrical tables. For example, below if you take their size 20 at high fan speed, they classify the motor HP at 1/30HP or 25W (output power). I’ve taken the subsequent columns to mean input power so the watts at 115V is then 57W which would make the motor is 44% efficient and that seems reasonable to me. The listed amps don’t necessarily equate to the same wattages, they are usually higher so my only theory is that this is the starting amps.
>
> I’d be interested in finding out what other have to say. I have tried talking to some local equipment reps without any luck.
>
> Aaron
>
> <image002.jpg>
>
>
> Aaron Smith, P.Eng
> M&R Engineering
>
> -----Original Message-----
> From: RobertWichert [mailto:robert at wichert.org]
> Sent: Friday, February 22, 2013 12:25 PM
> To: bldg-sim at lists.onebuilding.org; Scott Blunk
> Subject: [Bldg-sim] Fan Power
>
> This is a DOE-2 question, I think, but I am applying it to EnergyPro. I
> am asking here in the hopes that some will have a more in-depth
> knowledge of DOE-2 and how it relates to fan power. I am also hoping
> that some here will be able to reflect on the theory and application of
> fan power and energy as it relates to actual systems and modeling.
>
> When inputting indoor fan power, I have used many sources for the fan
> power. I sometimes use the motor nameplate, which I believe is too high
> in every case.
>
> I also sometimes use FLA or RLA, which I also do not believe are
> accurate, but sometimes give more realistic numbers.
>
> Some manufacturers give fan BHP at design conditions, which I find to be
> very helpful, but not everybody is that helpful.
>
> It has been suggested that I calculate the fan BHP using the theoretical
> formula *** Fan BHP = (cfm x static press "w.c.) / (6356 x fan
> efficiency) *** and then use a conservative fan efficiency (maybe 50%)
> for a good number. This gives a much lower value than the other
> methods, and I am trying to see if there is anything wrong with this
> approach.
>
> As I understand the usage, indoor fan power is divided by motor and
> drive efficiency to come up with fan energy. So the fan BHP is the
> starting point. Having this too high drives up fan energy, sometimes
> dramatically, and can influence the proposed case quite a bit if there
> are lots of fans, even small fans.
>
>
> Any thoughts on this approach would be very much appreciated.
>
>
>
> --
> Robert Wichert P.Eng. LEED AP BD&C
> +1 916 966 9060
> FAX +1 916 966 9068
>
>
>
>
>
>
>
> ===============================================
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130222/17f6d484/attachment-0002.htm>
More information about the Bldg-sim
mailing list