[Bldg-sim] Gross cooling capacity at ARI conditions
Nick Caton
ncaton at smithboucher.com
Thu Jan 10 10:04:13 PST 2013
I'm not terribly satisfied with the clarity of terminology in the example provided...
The basic concept is "gross (nominal) cooling energy" - "fan energy input" = "non-fan cooling energy"
Put another way, you can ultimately arrive at a cooling EIR (independent of fan energies) by subtracting the fan kW from the system total kW at ARI conditions.
Trying to present this using capacities instead of kW is only confusing the point they mean to make, as I understand it.
Hope that helps!
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Rasheed Ahmad
Sent: Thursday, January 10, 2013 6:43 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Gross cooling capacity at ARI conditions
Hello All,
>From the user's guide, the fan power should be removed from the standard EER
rating of packaged cooling systems.
A 15-ton packaged rooftop single-zone system having an EER of 8.6 (COP of
2.5) is
specified for a building. The following table gives the design
specifications. How should
this be modeled?
Equipment parameter Value
Net Cooling Capacity (Btu/h) 174,000
Total Packaged Unit Input Power (W) 20,128
EER 8.64
Gross Cooling Cap (ARI conditions) 182,000
The supply fan power is the difference between the gross and the net cooling
capacity.
So my Query is that Gross Cooling capacity ( ARI Condition ) is same for all Packaged system of any tonnage ??? Is it standard one or what ???? ........Like i have 1.5
ton of PTAC system, so for 1.5 ton of PTAC system also its gross cooling capacity is same 182,000????
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130110/9f877e4e/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130110/9f877e4e/attachment-0002.jpg>
More information about the Bldg-sim
mailing list