[Bldg-sim] PIU Temperature Schedule in eQuest
Robby Oylear
robbyoylear at gmail.com
Mon Jan 21 08:29:41 PST 2013
I agree that the help file language is a bit confusing. I've always set
this parameter to the same value that is used at the zone level heating
thermostat schedule and never thought twice about it.
For curiosity's sake, you could likely run an hourly report to determine
that the parallel fan is operating as you think it should.
To solve your problem, I usually just define a user-default expression of
#L("HEAT-TEMP-SCH"). This sets the parallel fan-powered schedule equal to
the zone thermostat schedule automatically.
On Mon, Jan 21, 2013 at 6:25 AM, Christopher Hadlock <
chadlock at fluentgroup.com> wrote:
> All,
>
> Does anybody understand what the zone-level temperature schedule does
> for a PIU system with parallel-PIU fan control (in eQuest)?
>
> My understanding is that for a PIU system, zone level fans (in a
> parallel configuration) are only activated during heating hours (is this
> true?) and draw return air from the plenum to mix with the primary air,
> thereby taking advantage of the heat in the plenum. It would be
> counterproductive to do this in cooling mode as the primary air is
> typically at 55F, much cooler than plenum air.
>
> If my assumption is correct, I am confused by the definition for the
> Temperature Schedule (called Zone-Fan-T-Sch in the help file), which reads:
> "Required if Zone: Terminal-Typ = PARALLEL-PIU. Takes the U-name of a
> schedule (type = temperature) that gives the zone temperature at which the
> terminal blower turns on. This temperature must be above the heating range."
>
> Why should this temperature be above the heating range? What heating
> range is this referring to? I would have thought the temperature would be
> the temperature BELOW which the fans turn on to provide additional
> heating...in other words, if you're trying to maintain 70F in the space,
> the fans would be activated at 69F or thereabouts. Does anyone know what
> this Temperature Schedule does exactly?
>
> Any insight is appreciated.
>
> Chris
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130121/52b56c33/attachment-0002.htm>
More information about the Bldg-sim
mailing list