[Bldg-sim] LEED EAP2 simulation of a building without HVAC system

韩星 foolishstar at 163.com
Fri Jul 12 20:28:41 PDT 2013


Dear Larry, 
Thanks a lot! It really helps me!
Xing






在 2013-07-12 21:00:40,"Larry Degelman" <ldegelman at suddenlink.net> 写道:

I’m not sure if this is helpful or not, but in Table G3.1 (Modeling Requirements for Calculating Proposed and Baseline Performance), Parts 10 (c) and (d) state the following:
 
c.  Where no heating system exists or no heating system has been specified, the heating system classification shall be assumed to be electric, and the system characteristics shall be identical to the system modeled in the baseline building design.
 
d.  Where no cooling system exists or no cooling system has been specified, the cooling system shall be identical to the system modeled in the baseline building design.
 
Regards,
 
Larry
===============================
Larry O. Degelman, P.E., BEMP, HBDP
Professor Emeritus of Architecture
Texas A&M University
===============================
 
From:韩星
Sent: Thursday, July 11, 2013 10:06 PM
To:bldg
Subject: [Bldg-sim] LEED EAP2 simulation of a building without HVAC system
 
Dear all,
In a LEED project, generally the design case needs to simulate the energy consumption as the designed HVAC system. However, if HVAC system does not be included in the design, how should I simulate to obtain the EAP2 and EAC1?
The HVAC system is left to the tenants to design and install.
Thanks!
Xing




_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130713/ad3b17e4/attachment-0001.htm>


More information about the Bldg-sim mailing list