[Bldg-sim] 2 Pipe System Heating/Cooling Change Over
    Graham Carter & Megan Lyall 
    hamnmegs at ozemail.com.au
       
    Tue Mar 19 03:47:13 PDT 2013
    
    
  
It has been a few years since I have used DOE-2.2 day to day.
I recall that the hours where loads (temperatures) not met are reported include any optimum start / night purge hours.  So if you have optimum start in your schedules you would typically get a few hundred hours reported even though conditions are being met during what we would call established building hours (i.e. hours when comfort conditions are expected).  As long as night purge / optimum start existed you would never be able to zero these hours.
I am unsure whether this has been tidied up in the most recent versions and I am also unsure whether it is across all SS reports.  If I recall correctly SS-R, SS-F and others were affected in this way.
Regards,
Graham
On 19/03/2013, at 9:34 AM, Demba Ndiaye wrote:
> Justin,
>  
> “Demand” is not adapted to 2-pipe loops. You should use either “Snap” or “Scheduled”.
>  
> Note that as James pointed out, it is very difficult to figure out the correct changeover period (if it exists!) when using a schedule.
>  
> Regards,
>  
> <image002.png> 
> 
> <image005.jpg>Demba Ndiaye, Ph.D., P.E., LEED AP BD+C, BEMP
> Senior Energy Analyst/Mechanical Engineer
>  
> Setty & Associates, Ltd.
>  
> MEP Design Engineering | Project Management
> |Construction Management | Design-Build Services | Commissioning
> |3040 Williams Drive, Suite 600 | Fairfax, VA 22031
> |Voice 703.691.2115 | Fax 703.691.8084 | cell 571.830.9913
>  demba.ndiaye at setty.com | www.setty.com
>  
> This e-mail and any files transmitted with it are confidential and are intended solely for the use of the individual or entity to whom they are addressed. If you are NOT the intended recipient or the person responsible for delivering the e-mail to the intended recipient, be advised that you have received this e-mail in error and that any use, dissemination, forwarding, printing or copying this e-mail is strictly prohibited.
>  
>  
>  
> From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Justin Chin
> Sent: Monday, March 18, 2013 5:22 PM
> To: James Hansen; bldg-sim at lists.onebuilding.org
> Subject: Re: [Bldg-sim] 2 Pipe System Heating/Cooling Change Over
>  
> I could model it as snap, but I would still get some unmet hours for certain days.  So far modeling as demand operation seems to be satisfying the thermostat settings in the summer, but I just can't figure out why heating isn't turned on.  And the model does have to meet LEED requirements. 
> 
> On Mon, Mar 18, 2013 at 5:12 PM, James Hansen <JHANSEN at ghtltd.com> wrote:
> I usually use a snap function to specify when the loop is in heating / cooling:
>  
> <image001.png>
>  
> By the way, I've modeled a few 2-pipe systems (in the DC area) before, and it is nearly impossible to get the unmet load hours below 300 for the average building (without significantly relaxing the thermostat setpoints, or having supplemental heating/cooling systems).  Hopefully you are not modeling this for LEED purposes!
>  
> GHT Limited
> James Hansen, P.E., LEED AP
> Senior Associate
> 1010 N. Glebe Road, Suite 200
> Arlington, VA  22201-4749
> 703-243-1200 (office)
> 703-338-5754 (cell)
> 703-276-1376 (fax)
> www.ghtltd.com
>  
> From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Justin Chin
> Sent: Monday, March 18, 2013 5:06 PM
> To: bldg-sim at lists.onebuilding.org
> Subject: [Bldg-sim] 2 Pipe System Heating/Cooling Change Over
>  
> Hello eQuesters,
>  
>   I am trying to model a two pipe system with a demand operation loop for a residential building in Maryland.  Currently, my two pipe system turns on cooling when the zones are calling for cooling as expected, however it never changes over to heating during the winter.  It is always either off, or on very rare occasions cooling, resulting in high unmet heating hours.  Can some one explain how the two pipe system determines when to change from heating to cooling mode?  
>  
> I've looked at the zones they are definitely below the heating throttling range.  Does eQuest take a sum of the room loads on the loop to determine to heat or to cool?
>  
> Your help is greatly appreciated.
> 
> Thanks!
> Justin
>  
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130319/6b497af3/attachment-0002.htm>
    
    
More information about the Bldg-sim
mailing list