[Bldg-sim] Per 90.1, mass wall or steel-framed wall?
Chris Baker
ChrisB at TWGI.com
Fri May 3 07:49:00 PDT 2013
Ramana,
Per Table G3.1 section 5b, the baseline is always a steel-framed wall
for Appendix G modeling. So you get to take credit for additional
thermal mass.
Chris Baker
AIA, PE, BEMP, BEAP,
LEED AP BD+C
THE WEIDT GROUP(r)
5800 Baker Road
Minnetonka, MN 55345
T 952.938.1588
F 952.938.1480
twgi.com <http://twgi.com/>
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Ramana Koti
Sent: Friday, May 03, 2013 9:37 AM
To: Bldg-Sim
Subject: [Bldg-sim] Per 90.1, mass wall or steel-framed wall?
Dear all,
For a LEED EAp2/EAc1 energy model, does the following above-grade wall
situation fall under a mass wall or a steel-framed wall in the baseline?
8" CMU wall (load bearing) with steel studs to the interior just to
create a cavity for the batt insulation etc.
Thanks,
Ramana Koti.