[Bldg-sim] Per 90.1, mass wall or steel-framed wall?
Nick Caton
ncaton at smithboucher.com
Fri May 3 10:10:51 PDT 2013
To round out the topic: Outside the context of LEED/Appendix G modeling (if you're concerned with prescriptive compliance), the threshold of what constitutes a mass wall is based on heat capacity (thermal mass), defined further in the 90.1 definitions.
I once looked hard at the issue and came away with this easy rule of thumb: any wall construction including a course of standard 4" brick exceeds the threshold and can be considered a mass wall. I would expect pretty much any wall including CMU to follow suit, filled or not.
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Ramana Koti
Sent: Friday, May 03, 2013 10:41 AM
To: Nathan Kegel
Cc: Bldg-Sim
Subject: Re: [Bldg-sim] Per 90.1, mass wall or steel-framed wall?
Thank you guys, that was helpful.
Ramana.
On Fri, May 3, 2013 at 11:11 AM, Nathan Kegel <nathan.kegel at iesve.com<mailto:nathan.kegel at iesve.com>> wrote:
Assuming it's new construction, of course.
[Description: IES]<http://www.iesve.com/>
Nathan Kegel
Project Manager
Business Development Manager
Minneapolis
T:
763 276 9981<tel:763%20276%209981>
M:
415 420 9314<tel:415%20420%209314>
http://www.iesve.com<http://www.iesve.com/>
**Design, Simulate + Innovate with the <Virtual Environment>**
Integrated Environmental Solutions Limited. Registered in Scotland No. SC151456
Registered Office - Helix Building, West Of Scotland Science Park, Glasgow G20 0SP
Email Disclaimer<http://www.iesve.com/disclaimer.html>
From: bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org> [mailto:bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org>] On Behalf Of Chris Baker
Sent: Friday, May 03, 2013 9:49 AM
To: Ramana Koti; Bldg-Sim
Subject: Re: [Bldg-sim] Per 90.1, mass wall or steel-framed wall?
Ramana,
Per Table G3.1 section 5b, the baseline is always a steel-framed wall for Appendix G modeling. So you get to take credit for additional thermal mass.
Chris Baker
AIA, PE, BEMP, BEAP,
LEED AP BD+C
THE WEIDT GROUP(r)
[cid:image003.gif at 01CE47F3.BD612B50]
5800 Baker Road
Minnetonka, MN 55345
T 952.938.1588<tel:952.938.1588>
F 952.938.1480<tel:952.938.1480>
twgi.com<http://twgi.com/>
________________________________
From: bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org> [mailto:bldg-sim-bounces at lists.onebuilding.org]<mailto:[mailto:bldg-sim-bounces at lists.onebuilding.org]> On Behalf Of Ramana Koti
Sent: Friday, May 03, 2013 9:37 AM
To: Bldg-Sim
Subject: [Bldg-sim] Per 90.1, mass wall or steel-framed wall?
Dear all,
For a LEED EAp2/EAc1 energy model, does the following above-grade wall situation fall under a mass wall or a steel-framed wall in the baseline?
8" CMU wall (load bearing) with steel studs to the interior just to create a cavity for the batt insulation etc.
Thanks,
Ramana Koti.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130503/829e39d6/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130503/829e39d6/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 2684 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130503/829e39d6/attachment-0005.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.gif
Type: image/gif
Size: 1199 bytes
Desc: image003.gif
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130503/829e39d6/attachment-0002.gif>
More information about the Bldg-sim
mailing list