[Bldg-sim] Baseline VAV OA vs Proposed DOAS OA
Wahid Hamed
wahid.hamed at gmail.com
Sat May 11 02:34:55 PDT 2013
Hi Donal,
As OA in the proposed model must equal the OA in the baseline model so you
have to use 13,160 CFM (better energy saving chance on the proposed than
10,216 CFM).
There are more details on Example 6-III "Calculation of Fan Power Energy,
Floor-by-Floor System" at ASHRAE 90.1-2007 User's Manual
Best Regards,
Wahid H. Mohamed, LEED AP BD+C ****
(+966)-5467 622 67
Mechanical Project Engineer, Energy Modeler
On Fri, May 10, 2013 at 5:32 PM, Dónal O'Connor <oconnor_dj at hotmail.com>wrote:
> Hi all,
>
> I'm looking for guidance on which number to use for my baseline OA when
> compared to the proposed system.
>
> The proposed HVAC system is DOAS - FCUs. OA requirements according to
> ASHRAE 62.1 are 10,216 cfm. However, to satisfy exhaust requirements, the
> total system ventilation, i.e. OA as it's a DOAS, is 13,160 cfm.
>
> Does the baseline OA need to equal 10,216 or 13,160 cfm?
>
> Thanks
>
> Dónal
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130511/7fb3b2fe/attachment-0001.htm>
More information about the Bldg-sim
mailing list