[Bldg-sim] 2 pipe FCU in EnergyPlus

Chandan Sharma csharma at fsec.ucf.edu
Mon May 20 13:11:30 PDT 2013


Hi Qinpeng,

Cooling coil availability schedule can be used to make it unavailable.

 From E+ IO Reference

Fan coil units can be 4-pipe or 2-pipe. For 4-pipe units there are 2 
supply pipes and 2 return
pipes. For 2-pipe units there is a single supply pipe and a single 
return pipe and the supply is
switched between hot and chilled water depending on the season. We model 
4-pipe units, but
the 4-pipe model can be used to model 2-pipe units by using the coil 
availability schedules to
make sure that either hot or chilled water is exclusively available.

Thanks,
Chandan

On 5/20/2013 4:01 PM, Qinpeng Wang wrote:
>
> Hi All,
>
> I have a question regarding EnergyPlus HVAC system modeling:
>
> How to model a 2 pipe FCU/UV in EnergyPlus because it seems to require 
> that I specify a cooling coil name which I don't have (I don't have a 
> cooling plant)?
>
> Thanks!
>
> -- 
>
> Qinpeng Wang, PhD Student
>
> College of Architecture
>
> Georgia Institute of Technology
>
> Atlanta, GA 30332-0155
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130520/693d8b4f/attachment-0002.htm>


More information about the Bldg-sim mailing list