[Bldg-sim] Really need some deep DOE-2 theology on this one..
Joe Huang
yjhuang at whiteboxtechnologies.com
Thu Oct 3 10:32:36 PDT 2013
Maybe I'm missing something here, but why not just change those roofs that you want
adiabatic to be Interior-walls and then change the INT-WALL-TYPE to be ADIABATIC ?
Wouldn't that take care of both the heat flow problem as well as the area numbers ?
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
http://weather.whiteboxtechnologies.com for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 3/10/2013 9:43 AM, Nick Caton wrote:
>
> I'm with Karen -- I don't think you can simply explain this one away to a LEED reviewer
> and will need to address/correct the issues you've identified
>
> If I'm not mistaken, "adiabatic" isn't an option for exterior surfaces however, at least
> through the eQuest detailed mode interface. You could make a distinct roof construction
> which has an impossibly low U-value to severely limit heat transfer (to/from exterior
> conditions), but that won't correct the roof area figures your reviewer is tuned into.
>
> In my opinion, the easiest reasonable thing to do would to assert (if you can) the
> thermostat setpoints are the identical between floors and therefore it's reasonable to
> not model heat transfer between floors, which means you can simply delete those
> "non-exposed" roofs. Re-defining those surfaces to be adiabatic ceiling/floor (using an
> interior wall construction) would have the same net effect except to define additional
> thermal mass for the associated spaces.
>
> The "partially correct" roof surface(s) on the other hand, which are both exposed and
> sandwiched, ought to be modified equally in both models to correct the exposed portion.
> How simple/involved this is depends on your project's geometries.
>
> Here's a procedure for a correcting a partially sandwiched, single surface roof. This
> is done in detailed mode and assumes wizard-based model assembly:
>
> -Navigate to 3D view, highlight the roof surface to be edited
>
> -Open properties window for that surface via the component tree or right-click context menu.
>
> -Identify the referenced space polygon (green text) in the surface properties
>
> -Scroll down to that polygon in the component tree, right click, create a new polygon,
> copy the one you identified -- name it anything you'll easily find in a long list.
>
> -Re-highlight that roof surface in the 3D view and open its properties window
>
> -Re-assign the polygon (green text) to the copied polygon with a unique name (will now
> be red text). Click Done. 3D view should look like nothing has changed at this point.
>
> oSave a copy of your project separately before proceeding!
>
> -Keeping a clear view of the roof section to be edited, now scroll down and double click
> on the new copied polygon to pull up its vertices.
>
> -From here, play around with manually removing vertices to identify which consecutive
> series bounds the sandwiched portion of the surface. You will observe which vertices go
> away or move in the 3D view behind if you delete/edit these inputs.
>
> -Determine whether you need to define any new vertices, to define the "seam" edge where
> exposed roof meets exposed wall. If so, experiment with editing a vertex to determine
> appropriate X/Y coordinates.
>
> -Once you've identified the vertices to remove and add, for eQuest stability reasons I
> try to edit existing polygon vertices before removing anything from the list (you'll
> typically end up with fewer vertices than you started). This is hard to put to words
> but bear with me: From the first vertex, identify the range which should remain (if
> any), then edit the following vertex points to any new coordinates you may have
> determined for additional points, then copy the series of vertices to remain from the
> end of the list up, then finally right-click and restore default to remove all vertices
> remaining in the list, starting from the bottom.
>
> -For context, I personally do not treat new/edited vertex coordinates super-precisely
> typically -- anything that looks close to right in the 3D view is good enough for LEED.
> Remember you'll be doing the same edits to both models. Don't get worked up over small
> seams/holes in the picture -- they don't cause roof leaks in in the model!
>
> Procedure for a multi-surface roof (one per space/plenum) is the similar except you do
> it for each partially sandwiched roof section (don't worry this gets quicker/easier
> after the first couple). Those fully-sandwiched sections can either be fully deleted
> per the above logic, or else re-defined as interior floor/ceiling surfaces if deemed
> necessary.
>
> Until you wrap up such polygon geometry edits, save separately and often, and run a
> simulation to test everything is working okay. I've had some mixed results doing such
> edits with eQuest interface open. You may see errors/cautions pop up that can be simply
> clicked through without consequence.
>
> When all is said and done, one piece of good news is you can save, close, and copy/paste
> all modified custom polygons between your baseline/proposed models, which makes doing
> the same edits on the other model as simple as re-assigning polygons (with 3D view up to
> check your work).
>
> ~Nick
>
> cid:489575314 at 22072009-0ABB**
>
> **
>
> *NICK CATON, P.E.*
>
> SENIOR ENGINEER
>
> Smith & Boucher Engineers
>
> 25501 west valley parkway, suite 200
>
> olathe, ks 66061
>
> direct 913.344.0036
>
> fax 913.345.0617
>
> www.smithboucher.com__
>
> *From:*bldg-sim-bounces at lists.onebuilding.org
> [mailto:bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *Karen Walkerman
> *Sent:* Sunday, September 29, 2013 5:11 PM
> *To:* Patrick J. O'Leary, Jr.
> *Cc:* bldg-sim at lists.onebuilding.org
> *Subject:* Re: [Bldg-sim] Really need some deep DOE-2 theology on this one..
>
> If the "roofs" don't have a zone as the outside boundary condition, then the model views
> them as roofs exposed to the exterior. You need to fix this. If the spaces on the other
> side have the same thermostat setpoints, then the easiest thing to do is set the roof
> type to "adiabatic". This will save you from having to define new polygons if the floor
> above has different zone shapes. For a roof that is only partially covered by the floor
> above, you need to create the new polygons. Sorry.
>
> --
> Karen
>
> On Sep 28, 2013 9:41 PM, "Patrick J. O'Leary, Jr." <poleary1969 at gmail.com
> <mailto:poleary1969 at gmail.com>> wrote:
>
> this sounds like you have multiple shells in one model for this to occur? i'm pretty
> sure equest views an exterior wall/roof as an exterior wall/roof even if it is bounded
> by an interior wall. i had this problem come up on one of my own models where i ended
> up having a building wing meet the building trunk & as i had put them in as 2 separate
> shells equest did not recognize the dividing wall where the wing met the trunk as being
> an interior wall & assigned it (via the wizard) an exterior wall definition. i didn't
> catch this until reviewing the unmet load hour ss-r & s-va reports & couldn't figure out
> why the load was so high. changed the definition of the wall to interior (with a door)
> in detailed mode and the unmet load hours went to zero and the load came down.
>
> my understanding (in my case) is that if you create multiple shells and place them with
> a common wall that you want to be an interior the shell rotations need to be zero, even
> if you have the separation between the two shells occur at a 45 deg angle (then ask mr.
> architect about that one).
>
> On 9/28/13 4:47 PM, John Aulbach wrote:
>
> Hi Gang:
>
> I need to elite for this one, and you know who you are..
>
> I am reviewing another party's eQuest model submitted for LEED. The reviewer noted that
> the roof area far exceeded the actual building footprint.
>
> Well, guess why? Somehow, the other party made several floors ROOFS instead of ceilings.
> I might be able to simply turn the exterior spaces into interior ceilings, but one roof
> (over an unheated underground garage) is partially uder the building and partially
> exposed to the "sidewalk/entrance" of the building.
>
> The BIG Kahuena is this..if a space is crammed next to an adjacent space and one of the
> spaces claims an Exterioir surface between them, does DOE-2 think that Exterior surface
> is seeing outdoor conditions? Or does it ignore such a thin and merely considers the
> heat transfer between the spaces (like the wall/roof is NOT exposed to the outdoors)?
>
> My approach is this (unless you disagree)..leave the Exterior wall/roof along and
> explain that the model (now in Detailed Edit form) would need major surgery to correct
> to show actual roof area. Having the "roofs" there versus floors will not change the
> thermodynamics of heat transfer.
>
> I yield to the floor.
>
> John Aulbach, PE
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG <mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20131003/819d962e/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20131003/819d962e/attachment-0002.jpeg>
More information about the Bldg-sim
mailing list