[Bldg-sim] Diversity factors
Jim Dirkes
jim at buildingperformanceteam.com
Wed Aug 13 09:20:32 PDT 2014
A couple more references:
· The ASHRAE 90.1 User Manual has many typical diversity tables
· The Title 24 Non-residential Alternative Compliance Manual http://www.energy.ca.gov/title24/2005standards/nonresidential_acm/
· (I have attached a spreadsheet which contains those schedules from a recent version, but I’ve lost track of which version)
James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com<http://www.buildingperformanceteam.com/>
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jeff Haberl
Sent: Wednesday, August 13, 2014 10:33 AM
To: Rathna Shree
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Diversity factors
FYI:
I think you’ll also find useful information in the ASHRAE Diversity Factor Toolkit – RP1093 as well as the papers:
Claridge, D., Abushakra, B., Haberl, J. 2003. “Electricity Diversity Profiles for Energy Simulation of Office Buildings (1093-RP),” ASHRAE Transactions-Research, Vol. 110, Pt. 1, pp. 365-377. ESL-PA-04-02-01 (February).
Abushakra, B., Haberl, J., Claridge, D. 2004. “Overview of Literature on Diversity Factors and Schedules for Energy and Cooling Load Calculations (1093-RP),” ASHRAE Transactions-Research, Vol. 110, Pt. 1, pp. 164-176. ESL-PA-04-01-01 (January).
Jeff
8=! 8=) :=) 8=) ;=) 8=) 8=( 8=) 8=() 8=) 8=| 8=) :=') 8=) 8=?
Jeff S. Haberl, Ph.D.,P.E.inactive,FASHRAE,FIBPSA,......jhaberl at tamu.edu<mailto:........jhaberl at tamu.edu>
Professor........................................................................Office Ph: 979-845-6507
Department of Architecture............................................Lab Ph:979-845-6065
Energy Systems Laboratory...........................................FAX: 979-862-2457
Texas A&M University...................................................77843-3581
College Station, Texas, USA, 77843..............................URL:www.esl.tamu.edu
8=/ 8=) :=) 8=) ;=) 8=) 8=() 8=) :=) 8=) 8=! 8=) 8=? 8=) 8=0
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Peter Simmonds
Sent: Wednesday, August 13, 2014 9:28 AM
To: Rathna Shree
Cc: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] Diversity factors
Dear all, here are my comments and suggestions.
I use the following to determine a diversity in a building. From the simulation model the number of occupants based on say one person per 10m2 ( one per 100sf) is 800. Then look at the fire Marshall report for the number of people allowed in the building, also look at the elevator calculations to see on how many occupants the elevators have been calculated to and lastly if there is a cafeteria or canteen see how many people have been used in the calculations?
For simplicity let's say the fire rating is 600 occupants then the simple diversity is 600/800 =75%
Peter Simmonds, Ph.D., ASHRAE Fellow and DL
Mobile US: +1-310-383-9911
Mobile HKG: +852-9845-4902
Mobile UK: +44 7711 926317
On Aug 12, 2014, at 11:09 PM, Rathna Shree <rathnashreep at yahoo.in<mailto:rathnashreep at yahoo.in>> wrote:
Hi Cheney/Bharath,
Thank you for the reply.
The fresh air is calculated and the system is sized as per ASHRAE 62.1 only.
I will elaborate the issue with an example. If the required cooling capacity after the heat load calculations is 1000 Tr, the diversity of around 80% will be considered for this 1000 Tr. The chillers are sized only for 800 Tr. In the simulation, this diversity considered by the designer will result in plant unmet. I tried reducing the plant unmet by reducing the occupancy, lighting and equipment loads by 20% in the schedules. But the 1000 Tr is calculated including the envelope and fresh air loads also. How to account the diversity from these loads?
Regards,
Rathnashree
On Tuesday, 12 August 2014 10:16 PM, Cheney <chenyu73 at gmail.com<mailto:chenyu73 at gmail.com>> wrote:
Well, I guess Rathna's question is the
'
conflict
'
between ASHARE 62.1 ventilation calc
(100% OA systems)
and
OA
system sizing/design by designer:
for DOA or single zone ventilation calc, diversity factor shall not be applied. However, taking school
building
as an example, HVAC system
could be 'downs
ized
'
according to the diversified occupants
when
designers believe the total number
of students and teachers
is fixed and they just move from one zone to the other.
Bear in mind,
DCV
/CO2 control
is
the key which is
commonly used in order to
accommodate
such "diversity"
.
My understanding is that v
entilation calc
without diversity
in this case is actually calculating the maximum OA
or sum of the diffuser flows
for each room
. From design point of view, two scenarios: 1. ventilation equipment can be reduced with respect to such diversity factor provided CO2 control is in the place. or 2. on the other hand, without CO2 control, conflict persists and equipment sizing has to follow ASHRAE 62.1 calculation.
Let me know your thoughts.
Best Regards,
Cheney
Connect with me and view my [http://press.linkedin.com/display-media/209/4] http://lnkd.in/bqQf52i
On Aug 12, 2014 4:24 AM, "Bharath Seshadri" <s.bharath at ntu.edu.sg<mailto:s.bharath at ntu.edu.sg>> wrote:
Hi Rathnashree,
Yes, it’s not easy for a core-and-shell building. We helped design a core-shell building recently. Here are some points we considered:
- What kind of tenants do you expect to occupy the space? Offices/Laboratories/Workshops etc?
- If its offices, you could take the same diversity as occupancy i.e. assuming you are using some kind of demand based ventilation control
- If its Labs/Workshops you could refer to design guides such as Labs21 or local standards
- But the best option would be to study metered data of buildings of the same function in your region to understand what an acceptable diversity factor for fresh air could be
Hope this helps. Do let me know if you need further references. Would be glad to help.
Regards, Bharath
<image001.gif>
Bharath SESHADRI | Research Associate | Energy Research Institute | Nanyang Technological University, Clean Tech One, 1 Cleantech Loop, #06-09, Singapore 637141 (Map)<http://maps.ntu.edu.sg/maps#q:CleanTech%20One> | Mob: (65) 9321-9723 Tel: (65) 6592-3284 GMT+8h | Fax: (65) 6316-3195 | Email:s.bharath at ntu.edu.sg<mailto:scchien at ntu.edu.sg> | Web: www.ntu.edu.sg<http://www.ntu.edu.sg/> & www3.ntu.edu.sg/erian/<http://www3.ntu.edu.sg/erian/>
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org>] On Behalf Of Rathna Shree
Sent: Tuesday, August 12, 2014 5:51 PM
To: bldg
Subject: [Bldg-sim] Diversity factors
Dear All,
In most of the core and shell projects, the HVAC consultant would have considered diversity factor on the overall cooling tonnage. While modelling, we will be able to comfortably take diversity on occupancy, equipment and lighting loads. But diversity on fresh air cannot be taken. Because of which the project may end up with plant unmet hours. Please let me know how to tackle the issue.
Regards,
Rathnashree
________________________________
CONFIDENTIALITY:This email is intended solely for the person(s) named and may be confidential and/or privileged.If you are not the intended recipient,please delete it,notify us and do not copy,use,or disclose its contents.
Towards a sustainable earth:Print only when necessary.Thank you.
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140813/63f1e261/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Appendix_5.4B_-_ACM_Schedules.xlsx
Type: application/vnd.openxmlformats-officedocument.spreadsheetml.sheet
Size: 1977306 bytes
Desc: Appendix_5.4B_-_ACM_Schedules.xlsx
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140813/63f1e261/attachment-0001.bin>
More information about the Bldg-sim
mailing list