The plug loads are the plug loads. The 25% is just a guidance value from USGBC/GBCI. I've been over and under this level numerous times without a problem.
If you've used the load estimated by the mechanical and/or electrical engineers and apply an appropriate schedule then it should be good enough.
When you're under the 25% threshold a text box will appear for you to explain why. Just state that you've modeled the plug loads as designed.
10 W/m2 sounds a little low for an office. If the owner has made a commitment to use Energy Star devices or laptops for everyone, then 10 W/m2 is plausible. Don't forget to include other equipment like servers/IT equipment, copiers and kitchen equipment (microwave, coffee maker, etc.)
Fred
Fred Betz  PhD., LEED AP (r)BD&C
Senior Sustainable
Systems Analyst
AEI | AFFILIATED ENGINEERS, INC.
5802 Research Park Blvd. | Madison, WI  53719
P: 608.236.1175 | F: 608.238.2614
fbetz at aeieng.com<mailto:fbetz at aeieng.com>  |  www.aeieng.com<http://www.aeieng.com/>
From: Chris Yates [mailto:chris.malcolm.yates at gmail.com]
Sent: Thursday, February 13, 2014 2:28 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Leed eac1 Plug loads
Dear bldg sim'rs
I'm a little concerned that the plug loads I've modelled in my offices are low and could leed to some unwanted usgbc comments.
I'm meeting the 25% requirement but the peak load in the offices is 10w/m2. Whilst i dont think this is overly optimistic the reviewers may think otherwise. Has anybody had experience of plug loads being queried in detail?
Many thanks
Chris
Sent from my Android device. Please excuse typos, etc.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140213/35a0a3d0/attachment-0001.htm>
    
    
More information about the Bldg-sim
mailing list