[Bldg-sim] Leed eac1 Plug loads
Hudon, Philippe
phudon at bpa.ca
Mon Feb 17 10:02:18 PST 2014
Karen,
You have the schedule in this pdf file.
Regards,
[cid:image001.jpg at 01CEFA41.CCA337B0]
Philippe Hudon_ing., M.Sc.A.
phudon at bpa.ca<mailto:smayer at bpa.ca>
De : Karen Walkerman [mailto:kwalkerman at gmail.com]
Envoyé : 17 février 2014 12:29
À : Hudon, Philippe
Cc : bldg-sim at lists.onebuilding.org
Objet : Re: [Bldg-sim] Leed eac1 Plug loads
Philippe,
That is a useful document. Thanks! Do you know where I can find the schedules that are referenced in the table? (A, B, C, etc)
Thanks again,
Karen
On Feb 14, 2014 4:37 PM, "Hudon, Philippe" <phudon at bpa.ca<mailto:phudon at bpa.ca>> wrote:
Hi,
In Canada's norms, there are this table as reference for the plug loads.
Regards,
[cid:image001.jpg at 01CEFA41.CCA337B0]
Philippe Hudon_ing., M.Sc.A.
phudon at bpa.ca<mailto:smayer at bpa.ca> | www.bpa.ca<http://www.bpa.ca> | t: 5143833747x2805<tel:5143833747x2805> | cell: 4187204339<tel:4187204339>
381 rue Belvédère, Alma, Qc, G8B 5Y9
Les informations contenues dans le courriel que vous venez de recevoir, y compris les pièces jointes, sont destinées à l'usage exclusif de la (ou des) personne(s) identifiée(s) comme destinataires et sont confidentielles. Si vous n'en êtes pas le destinataire, soyez avisé que tout usage en est interdit. Si vous avez reçu ce courriel par erreur, veuillez le retourner à l'expéditeur et le supprimer complètement de votre système informatique.
De : bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org> [mailto:bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org>] De la part de Nick Caton
Envoyé : 13 février 2014 16:36
À : Duggin, Cory; David Eldridge; bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Objet : Re: [Bldg-sim] Leed eac1 Plug loads
This matches my experience as well for plug loads.
I would only plan to itemize plug loads for LEED documentation if attempting to document an energy saving measure above and beyond 90.1 pertaining to receptacle loads (such as plug load circuit controls required by the upcoming title 24).
ASHRAE recommends 0.75 W/ft2 for office building receptacle power density in the user's manual for 90.1-2007 (for when you don't have better data to found the inputs on). 10W/m2 is approximately 0.93W/ft2 (if my math is right), so that's certainly within a reasonable range of expectations.
I do not anticipate you will have any issues. I've regularly documented exactly the value per the user's manual citing that as the source in my documentation with no further comment.
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036<tel:913.344.0036>
fax 913.345.0617<tel:913.345.0617>
www.smithboucher.com<http://www.smithboucher.com>
From: bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Duggin, Cory
Sent: Thursday, February 13, 2014 3:26 PM
To: David Eldridge; bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] Leed eac1 Plug loads
I've never had to provide an itemized list for equipment loads after simply telling them the receptacle loads were modeled as designed per space type.
Cory Duggin, EI
Energy Engineer I
TLC Engineering for Architecture
direct:
615-346-1939<tel:615-346-1939>
From: bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of David Eldridge
Sent: Thursday, February 13, 2014 3:24 PM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] Leed eac1 Plug loads
At lower than 25% levels GBCI likely will ask for an itemized list to show that you've considered all of the potential contributors. In addition to Fred's list, add elevators if these aren't separately modeled. Water coolers. Anything that shows up with a connection in the electrical plans.
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Grumman/Butkus Associates
From: bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Fred Betz
Sent: Thursday, February 13, 2014 3:17 PM
To: Chris Yates; bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] Leed eac1 Plug loads
Chris,
The plug loads are the plug loads. The 25% is just a guidance value from USGBC/GBCI. I've been over and under this level numerous times without a problem.
If you've used the load estimated by the mechanical and/or electrical engineers and apply an appropriate schedule then it should be good enough.
When you're under the 25% threshold a text box will appear for you to explain why. Just state that you've modeled the plug loads as designed.
10 W/m2 sounds a little low for an office. If the owner has made a commitment to use Energy Star devices or laptops for everyone, then 10 W/m2 is plausible. Don't forget to include other equipment like servers/IT equipment, copiers and kitchen equipment (microwave, coffee maker, etc.)
Fred
Fred Betz PhD., LEED AP ®BD&C
Senior Sustainable
Systems Analyst
AEI | AFFILIATED ENGINEERS, INC.
5802 Research Park Blvd. | Madison, WI 53719
P: 608.236.1175<tel:608.236.1175> | F: 608.238.2614<tel:608.238.2614>
fbetz at aeieng.com<mailto:fbetz at aeieng.com> | www.aeieng.com<http://www.aeieng.com/>
From: Chris Yates [mailto:chris.malcolm.yates at gmail.com]
Sent: Thursday, February 13, 2014 2:28 PM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] Leed eac1 Plug loads
Dear bldg sim'rs
I'm a little concerned that the plug loads I've modelled in my offices are low and could leed to some unwanted usgbc comments.
I'm meeting the 25% requirement but the peak load in the offices is 10w/m2. Whilst i dont think this is overly optimistic the reviewers may think otherwise. Has anybody had experience of plug loads being queried in detail?
Many thanks
Chris
Sent from my Android device. Please excuse typos, etc.
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140217/380aeac1/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 5712 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140217/380aeac1/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140217/380aeac1/attachment-0005.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: schedule.pdf
Type: application/pdf
Size: 93656 bytes
Desc: schedule.pdf
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140217/380aeac1/attachment-0002.pdf>
More information about the Bldg-sim
mailing list