[Bldg-sim] Claiming refrigerated casework savings for a LEED project
RobertWichert
robert at wichert.org
Wed Jan 22 14:58:52 PST 2014
Jim,
For the lights I would do a quick calculation of the Wattages of equal
illumination lighting. Whatever the case manufacturer would use in
their BASELINE models. I'm sure the LEDs are an upgrade, so just base
the savings on the wattages and the hours of operation. That one should
be easy.
You could basically do the same thing with the COP. As long as it is
for the entire system, you can use a reasonable load and just multiply
it out. I'd try that anyway. You might get shot down, but then you can
always come back with different.
I'm not so sure about the ECM fans. Where is the savings? If they are
variable speed, then there are some studies on variable speed fans
versus constant speed fans, but they should be application specific /
load profile specific. I have seen ECM fan coil fans that save
approximately nothing.
I believe that utilities give rebates and incentives for refrigeration
upgrades like these. Maybe the local utility does that. Maybe PG&E
does that. If so, they may be able to steer you to a paper.
Good luck!
Robert Wichert P.Eng. LEED AP BD&C
+1 916 966 9060
FAX +1 916 966 9068
===============================================
On 1/22/2014 2:32 PM, Jim Dirkes wrote:
>
> Dear Forum,
>
> I am modeling a supermarket which has made effort to install
> refrigerated casework that is more efficient than "normal" in three ways:
>
> . Casework lighting is LED instead of fluorescent
>
> . Evaporator fans use ECM motors and are demonstrably more
> efficient
>
> . The compressors have higher COP
>
> I did not realize that claiming savings from a "process" load also
> requires substantiation of the Baseline energy for the process load
> via comparison to several similar facilities or a published paper. I
> wish I knew that months ago!
>
> We have data from three other supermarkets owned by the same company,
> but these other examples are not identical. So far, all I can say is
> that:
>
> a) Manufacturer literature claims that LEDs used in their
> casework use ~ 65% less energy than fluorescent lights
>
> b) ECM fans use about 35% less energy in a manufacturer
> power comparison table
>
> c) The COP is better (I do not have detailed data yet)
>
> *This strikes me as a fairly weak argument, so I am asking you for
> suggestions or published data to strengthen the argument.*
>
> p.s., My last alternative is to ignore the process energy savings and
> make it the same for both models. I think the savings are substantial,
> however, and would rather find a way to claim them!
>
> BPT-e-mail-signature-template_readable-text
>
> "Attack me ... rather than the path I follow and which I point to
> anyone who asks me where I think it lies. If I know the way home and
> am walking along it drunkenly, is it any less the right way because I
> am staggering side to side?" Leo Tolstoy
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140122/25ebca83/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 23722 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140122/25ebca83/attachment-0002.png>
More information about the Bldg-sim
mailing list